[Equest-users] HVAC selection in LEED CI
Fleming, Joe
joe.fleming at tlc-eng.com
Wed Dec 8 06:41:28 PST 2010
To clarify the first model mentioned below, in your case, should be modeled as system #8 VAV systems with PFB's fed from the actual base building's chilled water system. (If there is no chiller then use DX systems, but the 3rd model based on ASHRAE will probably win out here and be the comparison model if no chiller is actually installed).
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer I
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image001.gif at 01CB96BC.163E22A0]<http://www.tlc-engineers.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fleming, Joe
Sent: Wednesday, December 08, 2010 9:37 AM
To: Mohammad Almasri; 'equest-users'
Subject: Re: [Equest-users] HVAC selection in LEED CI
Mohammed,
First, you should model the building system as it is installed (ignore the ASHRAE baseline here), including envelope.
You then have to do swap in the appropriate ASHRAE Baseline system for the CI area. That's 1 model.
In your proposed model you should model the actual system being installed in the CI portion. That's 2 models.
If the engineers are modifying the Base Building plant or systems in the design then in the 1st Baseline model you will swap in the appropriate ASHRAE appendix G systems for the replaced equipment.
You also have to model another building based entirely on ASHRAE 90.1 and Appendix G, using the typical modeling procedures that you would use for a LEED NC project. That's 3 models.
So, you will have 3 eQuest models or you can use parametric runs to eliminate one of the models, but you will have 3 sets of results that you need to submit to the USGBC.
You will then use the more efficient of the 2 Baseline models for your energy comparison.
I have not had a CI model reviewed yet, but this has been my interpretation thus far.
It is very time consuming. Maybe going for EAC1.3 Option 1 would save some time?
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer I
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image001.gif at 01CB96BC.163E22A0]<http://www.tlc-engineers.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mohammad Almasri
Sent: Wednesday, December 08, 2010 8:56 AM
To: 'equest-users'
Subject: [Equest-users] HVAC selection in LEED CI
Dear All,
I am working on LEED CI certification for office building (area 5382sf) . I have a problem to select the baseline HVAC system to calculate the saving for EAC1.3 In the LEED CI. The rating system provide the modeler the ability to choose the simulation method (ECB Section 11 or Performance rating).
But in case I used the performance rating method , what is the baseline system?
It will be System 4- PSZ-HP (depending on that the area is below 25,000sf)
OR
System 8 -VAV/with PFP box depending on that the office is in tower ,and the whole tower area is more than 15,000sf (in this case ,a separate meter will use to calculate the office energy usage)
Any advice
Regards,
------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
Mohammad Al-Masri
Simulation Engineer
LEED AB BD+C , CAPM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101208/82732a15/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101208/82732a15/attachment-0002.gif>
More information about the Equest-users
mailing list