[Equest-users] equest crashing on chilled water loop primaryselection

RobertGChronic at Eaton.com RobertGChronic at Eaton.com
Mon Dec 20 09:32:09 PST 2010


Since this is a campus connection, I only wanted the load of the chilled
water and not necessarily size a chiller plant.  I thought the easiest
way was to "replace" the plant with a meter and have the meter tally up
the loads.  I certainly would welcome any feedback if there are better /
easier ways to model a campus chilled water connection.

 

Thanks!

 

From: Shaun Martin [mailto:smartin at shaunmartinconsulting.com] 
Sent: Wednesday, December 15, 2010 6:12 PM
To: Chronic, Robert G; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] equest crashing on chilled water loop
primaryselection

 

You only seem to have a chilled water meter attached to this loop - no
primary equipment (chiller) so there is nothing to size to.

 

 

 

Shaun Martin LEED AP

Principal

Shaun Martin Consulting

Suite 200 - 420 West Hastings Street

Vancouver BC   V6B 1L1

604-789-1095

smartin at shaunmartinconsulting.com
<mailto:smartin at shaunmartinconsulting.com> 

member CAGBC, ASHRAE

 

 

 

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
RobertGChronic at Eaton.com
Sent: Wednesday, December 15, 2010 2:29 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] equest crashing on chilled water loop
primaryselection

I am having an issue with equest crashing.  The error is associated with
the subtype being secondary for the chilled water loop, however, when I
switch it back to primary, I immediately get kicked out of equest.   I
have attached the screenshot of equest and the chilled water loop
appears to be nested.  I am not sure how this exactly happened, I was
attempting to redefine the chilled water loop.  Here is the excerpt from
the bdl file.  Is there any way to edit outside of equest interface so I
can alleviate the crashing??

 

 

     *3099 * "Chilled Water Loop" = CIRCULATION-LOOP

     *3100 *    TYPE             = CHW

     *3101 *    SUBTYPE          = SECONDARY

     *3102 *    LOOP-DESIGN-DT   = 15

     *3103 *    SIZING-OPTION    = PRIMARY

     *3104 *    PIPE-HEAD        = 55

     *3105 *    PRIMARY-LOOP     = "Chilled Water Loop"

     *3106 *    LOOP-OPERATION   = DEMAND

     *3107 *    DESIGN-COOL-T    = 45

     *3108 *    COOL-SETPT-CTRL  = FIXED

     *3109 *    LOOP-PUMP        = "CHW Loop Pump"

     *3110 *    HEAD-SETPT-CTRL  = FIXED

     *3111 *    HEAD-SETPT       = 30

     *3112 *    ..

*ERROR******************************************************************
**********************

*ERROR*****Chilled Water Loop cannot be specified as a PRIMARY-LOOP due
to

            incorrect SUBTYPE; valid PRIMARY-LOOP must have a SUBTYPE of
PRIMARY

 

 

Thanks!

 

 

Robert G. Chronic

Cx Team Leader

Energy Solutions Group

E M C Engineers, Inc.

Eaton's Electrical Services & Systems
408 West University Avenue, Suite 402
Gainesville, FL 32601
tel: +1 352 327-9358 ext. 300
mobile: +1 352 275-7417

fax: +1 352 327-9358

RobertGChronic at eaton.com
www.eaton.com <http://www.eaton.com/> /energysolutions

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101220/af7c7fe7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101220/af7c7fe7/attachment-0002.jpeg>


More information about the Equest-users mailing list