[Equest-users] Outside airflow (eQuest Users group)
Karen Walkerman
kwalkerman at gmail.com
Wed Feb 24 06:56:48 PST 2010
I have always sized the outdoor air to be the same in the proposed and
baseline buildings. There is a section in Appendix G that specifically
directs the modeler to do this. I have had a number of buildings approved
using this method.
--
Karen
On Wed, Feb 24, 2010 at 9:06 AM, Tomlinson, Scott <stomlinson at smma.com>wrote:
> Thank you to those who helped with my previous outside air question. I
> now understand how the outside air is controlled, I’m just not sure how I
> should be setting it. ASHRAE 90.1 – 2004 dictates that the minimum outdoor
> air ventilation rates should be the same for the design and baseline
> building, but one of our LEED review comments is that our baseline model
> should be modeled base on ASHRAE 62.1 – 2004 requirements. It seems that if
> I let eQuest size my OA based on ASHRAE 62.1 I won’t match my design
> building OA rates (in this case, 100%). Also, if I let eQuest size my OA
> based on the 100% OA rate of my design building I will be over ASHRAE 62.1
> requirements.
>
> What method of outside air sizing have y’all been using for your models,
> and have you been approved by USGBC with the method?
>
>
>
> - Thank you,
>
>
>
> __________________________________________
>
> *Scott Tomlinson, PE, LEED-AP*
>
> Mechanical
>
> *Symmes Maini & McKee Associates, Inc.*
>
> 1000 Massachusetts Avenue, Cambridge, MA 02138
>
> t: 617.520.9438
>
> [image: http://intranet/Images/USGBC.jpg]
>
>
>
> f: 617.354.5758
>
> stomlinson at smma.com <STomlinson at smma.com>
>
> www.smma.com
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100224/67fad291/attachment-0001.htm>
More information about the Equest-users
mailing list