[Equest-users] Circulation Loop Warnings
Bishop, Bill
wbishop at pathfinder-ea.com
Wed Feb 10 08:25:01 PST 2010
Katie,
If you don't enter loop PIPE-HEAD the default will be 21.6' (per the
help menu), then coil and equipment head is added. Adjust these to match
the specified pump performance. Hopefully that will take care of some of
those warnings.
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Katie
Tuttle
Sent: Wednesday, February 10, 2010 10:29 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Circulation Loop Warnings
Has anyone been able to resolve warnings that occur with circulation
loops? Please see attached for simulation warnings.
Thanks,
Katie
This email and any files transmitted with it are confidential and
are intended solely for the use of the individual or entity to whom
they are addressed. This communication represents the originator's
personal views and opinions, which do not necessarily reflect those of
Henderson Engineers, Inc. If you are not the original recipient or the
person responsible for delivering the email to the intended recipient,
be advised that you have received this email in error, and that any use,
dissemination, forwarding, printing, or copying of this email is
strictly
prohibited. If you received this email in error, please immediately
notify administrator at hei-eng.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100210/598f89cc/attachment-0002.htm>
More information about the Equest-users
mailing list