[Equest-users] Modeling landfill gas as a fuel

Bishop, Bill wbishop at pathfinder-ea.com
Mon Jul 26 07:30:49 PDT 2010


Jeff,
 
The CG plant has implications for both LEED EAc1 and the renewables
credits EAc2 and EAc6. For EAc1, you will need to determine how much
energy the CG plant will provide to the project. You will also need to
figure out the utility rate. Preferably, the owner/operator of the CG
plant will break up the billing into fuel and other costs. (Maintenance
and capital costs should not figure into the fuel cost for EAc1
calculation.) You will then have three utility rates (and three eQUEST
meters) - grid-provided electricity, landfill gas, and backup heating
fuel. Your baseline energy cost will use the rates for grid electricity
and backup heating fuel only.
 
I would try doing everything for the EAc1 calculation in eQUEST. Create
an electric generator of type "engine generator", assign it to a new
fuel meter, and assign it to the building electric meter. Electric
meters have a COGEN-TRACK-MODE that you use to set the control mode for
the CG plant. You can also assign a HW, WLHP or DHW loop to recover
exhaust heat. All of the electric end-use consumption provided by the CG
plant will show up as fuel consumption on your new fuel meter in the
eQUEST reports (such as BEPU).
 
For the renewables question, I disagree with Peter and think credit
should be taken for EAc2 - On-Site Renewable Energy, not EAc6. The
energy is produced on site, and landfill gas is an eligible renewable
source. You just need to account for the cost of the fuel as described
above for EAc1. Note, however, that I have not yet tried claiming this
for a LEED submission.
 
Best regards,
Bill
 
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter
Hillermann
Sent: Monday, July 26, 2010 10:07 AM
To: 'Jeff Ross-Bain'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Modeling landfill gas as a fuel
 
Energy that is purchased from a third party is EA credit 6 Green Power
and the third party needs to be able to prove that they have REC's
(renewable energy certificates) in order for it to count. Renewables go
toward the project be it building or whatever and have to be purchased
by the building owner. What I was told is that you are not allowed to
profit off your renewable energy if you are going to use it toward LEED
for a project. In order for it to count as renewable I think that the
owner of the site would have to give it to the building owner for free.
Call USGBC and ask them to interpret it for you to see. I usually call
the USGBC if I have questions and I do not understand. I do the same
with building code because you never know how the official interprets it
versus one of us that is doing the project.
 
In order to get EA credit 6 you have to purchase at least 35%  of your
annual electrical consumption from this third party and it is calculated
from the energy model you made in EA credit 1 or you have to go to the
US department of energy commercial buildings energy consumption survey
database to determine the estimated electricity use.
 
This is how I have interpreted the LEED manual.
 
Thanks,
 
PETER HILLERMANN
 
peterh at westallarchitects.com
 
westall
architects
3404 pierce drive
chamblee, georgia 30341
 
o 770.458.4113
f  770.458.5352
c 678.898.2936
 
westallarchitects.com
  
 
 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Ross-Bain
Sent: Friday, July 23, 2010 4:41 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling landfill gas as a fuel
 
Hi All,
 
I am a little stuck on an approach and wanted to get some guidance from
the eQUEST greats. I have a project that is installing a cogeneration
plant (CG) that will use landfill gas from a nearby landfill.
 
The cogeneration plant is installed on site and all energy generated by
the plant is used on site. However, the operator / owner of the
cogeneration plant, a third party, sells the energy to the building
owner.  
 
On the documentation side, would one use the exceptional calculation
method or the renewable energy section (LEED Online Template v2.2)?
Usually, the renewable energy does not have a "purchased" component as
in a utility. 
 
How would one go about getting credit for the amount of energy used from
this landfill gas cogeneration plant when that energy is purchased?
 
Thanks for your help.
 
Regards.
 
Jeffrey G Ross-Bain, PE, LEED, BEMP
Ross-Bain Green Building, LLC
404-228-2893
 
P Build Green...Save Time
 
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100726/eddcb40c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100726/eddcb40c/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3226 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100726/eddcb40c/attachment-0002.jpeg>


More information about the Equest-users mailing list