[Equest-users] eQuest: SEER to EIR??

Brett Fero bfero at robsonwoese.com
Thu Jun 17 10:44:50 PDT 2010


Peter,

If you replace with following to the Cooling EIR calculation in the middle of the page, the values will be correct for the AC EIR calculations.

Cooling EIR = ((1/EER)-0.012167)/((1/3.413)+0.012167)  (note the additional parenthesis in the numerator)
                EIR =  ((1/11)-0.012167)/((1/3.413)+0.012167) = 0.258
This equation is comparable to the EIR equation at the top of the page.

However, when given a SEER, I find a difference in the results.

EER = SEER x 0.778 + 1.4 = 13 x 0.778 + 1.4 = 11.514

EIR = ((1/11.514) - 0.012167)/((1/3.413)+0.012167) = 0.2447, not your Wizard value of 0.2507


Brett Fero, P.E., LEED AP
RobsonWoese Inc.
Salina Meadows Office Park
301 Plainfield Road, Suite 180
Syracuse, NY 13212
Phone:   315-445-2650
Fax:  315-445-0958
bfero at robsonwoese.com<mailto:bfero at robsonwoese.com>

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter Hillermann
Sent: Thursday, June 17, 2010 11:22 AM
To: 'Josh Greenfield'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest: SEER to EIR??

I have the same question as Josh. My value from the wizard is coming out different from the equation. Even when calculating EER to EIR.

Example:
Wizard = EER 11 = 0.258
Calculation = EER 11 =0 .31 (which actually is the default value in my model when I fire it up)

Wizard = EER 12.5 =0.2223
Calculation = EER 12.5 = 0.27

Wizard = SEER 13 = 0.2507
Calculation = SEER 13 = 0.296

However in my calculations there is a 0.05 difference from wizard to calculation. (Obviously missing something) Should I just use the wizard values and be done with it?

Thanks,

PETER HILLERMANN

peterh at westallarchitects.com<mailto:peterh at westallarchitects.com>

westall
architects
3404 pierce drive
chamblee, georgia 30341

o 770.458.4113
f  770.458.5352
c 678.898.2936

westallarchitects.com
[cid:image001.jpg at 01CB0E22.285C0FB0][cid:image002.gif at 01CB0E22.285C0FB0]



From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Josh Greenfield
Sent: Tuesday, June 15, 2010 4:02 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest: SEER to EIR??

Sorry to be beating a dead horse...

the attached document has been floating around the boards for awhile in regards to how an entered EER value in the Wizard gets converted to the Cooling-EIR value in the Detailed Edit mode, and after doing a few EER value tests, I can confirm it works...

I've also found in various emails the conversions on the heat pump heating side of COP and HSPF to Heating-EIR, and those work too after testing various values in the Wizard...
Heating EIR = (1/(COP*3.413)-0.012167)/((1/3.413)-0.012167)
Heating EIR = (1/((HSPF*0.28+1.13)*3.413)-0.012167)/((1/3.413)-0.012167)

But I just can't get the SEER to EER conversion from the document (EER = SEER x 0.778 + 1.4) to work.  I'm assuming that the converted SEER to EER value then gets put into the working equation from that PDF of Cooling-EIR = ((1/EER)-0.12167)/((1/3.413)+0.012167)).

As an example...if you put in a 13 SEER into the Wizard, a 0.2507 Cooling-EIR value is calculated in the Detailed Edit mode, but if you use the SEER to EER (13 SEER would equal a 11.514 EER) and then the EER to EIR equations, it says EIR should be 0.2447.

Any help/suggestions would be great...hopefully it's just a math error on my part.

Josh Greenfield, PE, REP, LEED AP
Energy Services Manager
Associate Vice President
312.242.6392 Direct
jgreenfield at primerachicago.com<blocked::mailto:jgreenfield at primerachicago.com>
[cid:image003.jpg at 01CB0E22.285C0FB0]
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.606.0415 Fax
http://www.primerachicago.com

________________________________
This e-mail message has been scanned for Viruses and Content and cleared by MailMarshal
________________________________

________________________________________________________________________
This Email has been scanned for all viruses by PAETEC Email Scanning Services, utilizing MessageLabs proprietary SkyScan infrastructure. For more information on a proactive anti-virus service working around the clock, around the globe, visit http://www.paetec.com.
________________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/7af4e0a8/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3222 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/7af4e0a8/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 2436 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/7af4e0a8/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1879 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/7af4e0a8/attachment-0003.jpg>


More information about the Equest-users mailing list