[Equest-users] Understanding Floors

Patrick J. O'Leary, Jr. poleary1969 at gmail.com
Mon Jun 21 11:45:31 PDT 2010


perhaps the question is "are you referring to a zone or a zone group?"

in the ddwizard you can specify multiple zones into a zone group.  so if 
every space, i.e. every room, is it's own zone, then you could add 
multiple spaces to a zone group.  otherwise you're just making a thermal 
zone composed of multiple spaces.  as far as i know.

On 6/21/10 11:35 AM, Pasha Korber-Gonzalez wrote:
> I'm with Vik- I thought it was only one space to one zone, but if 
> someone has a new way of things, please share...
> pkg
>
> On Mon, Jun 21, 2010 at 12:11 PM, Sami, Vikram 
> <Vikram.Sami at perkinswill.com <mailto:Vikram.Sami at perkinswill.com>> wrote:
>
>     Nick,
>
>     How do you group multiple spaces in one zone? I always thought you
>     could do only one space per zone.
>
>     *Vikram Sami*, LEED AP
>
>     Sustainable Design Analyst
>
>     1382 Peachtree St. NE, Atlanta, GA 30309
>
>     t: 404-443-7462    f: 404.892.5823     e:
>     vikram.sami at perkinswill.com <mailto:vikram.sami at perkinswill.com>
>     www.perkinswill.com <http://www.perkinswill.com/>
>
>     *Perkins+Will.* Ideas + buildings that honor the broader goals of
>     society
>
>     *From:* equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>
>     [mailto:equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
>     *Nick Caton
>     *Sent:* Monday, June 21, 2010 2:00 PM
>
>     *To:* Peter Hillermann; equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* Re: [Equest-users] Understanding Floors
>
>     Hey Peter,
>
>     If by “stack” you mean place one space geometrically over another,
>     the answer is yes.  If you mean to ask whether zones can group
>     spaces in different elevations, the answer is also yes.
>
>     However, I would like to hammer out your wording again to be sure
>     we’re on the same page!  I think you meant to ask “Can you stack a
>     space in a shell?”  Spaces are normally “inside” shells in a
>     geometrical sense, as they are generally within the shell
>     footprint/boundaries.
>
>     Zones, in contrast, have nothing to do with geometries – they are
>     simply groupings of spaces with some extra HVAC/airflow properties
>     tacked on.  Those spaces could be all over the place – at
>     different elevations, within different shells… pretty much any
>     combination from my experience.
>
>     Best of luck!  If you are getting tripped up, remember a picture
>     is worth a thousand questions (?)…
>
>
>     ~Nick
>
>     PS to all:  The SD/DD Wizards are, in my mind, kinda misleading
>     with regard to helping new users understand the distinction
>     between “space” & “zone.”  Some work in detailed mode will
>     eventually lead you to understand, but the Wizard screens
>     inconsistently interchange the terms and may cause others
>     confusion in the long run… See my description below for a simple
>     breakdown if you are cutting your teeth on eQuest ;).
>
>     cid:489575314 at 22072009-0ABB**
>
>     * *
>
>     *NICK CATON, E.I.T.***
>
>     PROJECT ENGINEER
>
>     25501 west valley parkway
>
>     olathe ks 66061
>
>     direct 913 344.0036
>
>     fax 913 345.0617
>
>     /Check out our new web-site @ /www.smithboucher.com
>     <http://www.smithboucher.com/>_ _
>
>     *From:* Peter Hillermann [mailto:peterh at westallarchitects.com
>     <mailto:peterh at westallarchitects.com>]
>     *Sent:* Monday, June 21, 2010 12:40 PM
>     *To:* Nick Caton; equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* RE: [Equest-users] Understanding Floors
>
>     Nick,
>
>     Thanks again. Can you stack a space in a zone?
>
>     Thanks,
>
>     *PETER HILLERMANN*
>
>     peterh at westallarchitects.com <mailto:peterh at westallarchitects.com>
>
>     *westall*
>
>     *architects*
>
>     3404 pierce drive
>
>     chamblee, georgia 30341
>
>     o 770.458.4113
>
>     f  770.458.5352
>
>     c 678.898.2936
>
>     westallarchitects.com <http://westallarchitects.com/>
>
>     *From:* Nick Caton [mailto:ncaton at smithboucher.com
>     <mailto:ncaton at smithboucher.com>]
>     *Sent:* Monday, June 21, 2010 12:33 PM
>     *To:* Peter Hillermann; equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* RE: [Equest-users] Understanding Floors
>
>     Peter, I think you might be leading yourself into some unnecessary
>     confusion with your word choices…
>
>     eQuest has 3 distinct entities:
>
>     - _Shells_ are simply groups of spaces
>
>     - _Spaces_ are geometrical volumes, which may or may not have
>     floors, walls, ceilings, windows, etc. tied to them.  Internal
>     loads / daylighting / occupancies are attributed to spaces.
>
>     - _Zones_ are simple entities that include one or more spaces,
>     with additional HVAC attributes like thermostat and airflow
>     specifics.
>
>     You’re using “floors” to interchangeable discuss all the above, it
>     seems.  For clarity when discussing eQuest, “floors” are merely
>     the constructions we walk on, normally one attribute of a “space.”
>
>     All that said, it’s entirely possible to model a “box within a
>     box,” as you’re describing.  You are limited in the wizards (by
>     their nature) with regard to defining zones/footprints… the best
>     approach depends on the nature of the space footprints you want to
>     model.  If it’s very simply two stacked cubes enclosed within a
>     larger cube, I’d personally model one shell, with one space carved
>     out of the middle.  Then I’d use the detailed mode to shrink that
>     space volume and partition/ceiling dimensions to match the first
>     floor office, then copy the entire space and its componenents for
>     the second floor.  I’d adjust the largest cube’s volume (it’s a
>     space property) to correct the conditioned volume, and be sure all
>     partitions are correctly associating the three spaces together… 
>     With all spaces sorted out, ensure your three spaces are correctly
>     grouped with regard to “zones,” for association with your HVAC
>     system(s).
>
>     Clear as mud =)?
>
>     * *
>
>     *~Nick*
>
>     * *
>
>     cid:489575314 at 22072009-0ABB**
>
>     * *
>
>     *NICK CATON, E.I.T.***
>
>     PROJECT ENGINEER
>
>     25501 west valley parkway
>
>     olathe ks 66061
>
>     direct 913 344.0036
>
>     fax 913 345.0617
>
>     /Check out our new web-site @ /www.smithboucher.com
>     <http://www.smithboucher.com/>_ _
>
>     *From:* equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>
>     [mailto:equest-users-bounces at lists.onebuilding.org
>     <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
>     *Peter Hillermann
>     *Sent:* Monday, June 21, 2010 10:56 AM
>     *To:* equest-users at lists.onebuilding.org
>     <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* [Equest-users] Understanding Floors
>
>     To All,
>
>     I just want to make sure I understand the properties behind
>     floors. If you have a square building volume with a smaller square
>     inside it that has 2 levels. EG:- an atrium as main space with 2
>     levels that are offices. There will be a total of 3 floors in your
>     model. Atrium floor, first floor office and second floor office.
>     Each of these will have a designated floor to floor height. You
>     cannot put one zone inside another on the same floor.
>
>     Is this correct?
>
>     Thanks,
>
>     *PETER HILLERMANN*
>
>     peterh at westallarchitects.com <mailto:peterh at westallarchitects.com>
>
>     *westall*
>
>     *architects*
>
>     3404 pierce drive
>
>     chamblee, georgia 30341
>
>     o 770.458.4113
>
>     f  770.458.5352
>
>     c 678.898.2936
>
>     westallarchitects.com <http://westallarchitects.com/>
>
>     e-signatureUSGBC-Logo
>
>
>     This email and any files transmitted with it are confidential and
>     intended solely for the addressee. If you are not the named
>     addressee you should not disseminate, distribute, copy, or alter
>     this email.
>
>     _______________________________________________
>     Equest-users mailing list
>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>     To unsubscribe from this mailing list send  a blank message to
>     EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>     <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>    

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100621/f456b86e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 49352 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100621/f456b86e/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100621/f456b86e/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100621/f456b86e/attachment-0005.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100621/f456b86e/attachment-0001.gif>


More information about the Equest-users mailing list