If the insulated envelope values that you have entered are correct, then
I would suspect that both the outside ventilation air that is entering
the building through control and air leakage are to low and that likely
the internal heat gains from equipment from computers, etc. are too low.
The fact that the actual use is higher in both the winter and summer
would indicate the outside air, but I think if you just increase only
the outside air and not the internal electrical use numbers also, then
you'll likely see too big of peak in both the summer and winter.  Good
luck, it is also fun trying to match an actual energy use pattern on an
existing building.
 
Thanks,
David A. Bastow 
McClure Engineering, Inc.  
507 Main Avenue West
Post Office Box 1404
Twin Falls, Idaho   83303-1404
<mailto:dbastow at mcclure-engineering.com> 
Web Site:  www.mcclure-engineering.com
<http://www.mcclure-engineering.com/> 
 
 

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vaziri,
Mo (ON0F)
Sent: Tuesday, March 16, 2010 9:20 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Existing building simulation



If we are doing a simulation for an existing building and the actual
electricity consumption does not match with the simulation, how can we
adjust/calibrate it?

 

The snapshot shows the actual (blue graph) vs. simulation.

 

 

 

Regards,

Mo Vaziri 

 

                                             Honeywell 

Mo Vaziri, P. Eng. , LEED AP, CEM
Design Build / Energy Engineer 
Honeywell Building Solutions - Canada

85 Enterprise Boulevard, Suite 100

Markham, Ontario, L6G 0B5 
*       Phone: (289) 333-1340 
*                 Fax:      (289) 333-1333 
*       Cell:     (416) 527-4692 
*       mohammad.vaziri at honeywell.com
<mailto:pmohammad.vaziri at honeywell.com>  

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/77f2bdfd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 11977 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/77f2bdfd/attachment.gif>


More information about the Equest-users mailing list