[Equest-users] eQuest - FCU with DOAS

James Hansen JHANSEN at ghtltd.com
Mon Mar 1 08:15:35 PST 2010


I haven't had a chance to look at your .inp file, but when you are creating a DOAS system, make sure that you at least do the following:

1) Make sure the fan schedule is forced off at night and setback times.
2) Make sure the throttling range for the dummy zone thermostat is at least 4 degrees (I usually use 6).
3) Make sure that the heating/cooling schedules that the dummy zone follows are set to something like 120 degrees cooling and 20 degrees heating after hours, just to make sure that a call for heating/cooling doesn't show up in your report, and mess up the unmet load hours.


Just looked at your file:  you need to specify some sort of minimum OA control or minimum air schedule for the FCUs (I think).  Right now nothing shows up.

Also, why is the DOAS system serving so many "dummy" zones?  I *think* your DOAS system is EL1 Sys1 (SZRH), yet it is serving 20+ zones.  I'm confused...

GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA  22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com



-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Marcus Eliason
Sent: Monday, March 01, 2010 11:04 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest - FCU with DOAS


Hello,

I am trying to model a building with FCUs and a DOAS to deliver outdoor air to the individual zones.  I have put in the dummy zones for the DOAS system, modeled as a single air handler with chilled and hot water coils. I have changed the walls of the dummy zone to air walls, specified the DOAS to get OA flow as sum of all zones and for the FCUs to get OA from the DOAS.  When I run the model, I get a lot of unmet hours corresponding to the dummy zones and the DOAS system.  I have tried but cannot seem to turn off the return air path for the DOAS (since it is 100% OA) and have specified the minimum OA fraction for the DOAS as 1.  I am not sure if the unmet hours means that my DOAS is not adequately cooling the OA load or if it something else.
Also, my "pump & aux" energy in the model seems very high for a building that only has 3 pumps.  Can someone familiar with modeling DOAS shed any light on what might be causing some of these problems.  I have attached the .inp and .pd2 files for reference.

Thanks,

Marcus Eliason



The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments.  Thank you.






More information about the Equest-users mailing list