[Equest-users] External Shading and Self-Shading

Nick Caton ncaton at smithboucher.com
Tue Mar 23 07:22:03 PDT 2010


Bill/Luke:

 

Thanks!  I felt certain this was there but I guess my eyes were
selectively screening that line for some reason J.

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com] 
Sent: Tuesday, March 23, 2010 9:13 AM
To: Nick Caton; Wilson, Luke; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] External Shading and Self-Shading

 

Nick,

 

ASHRAE Standard 90.1, 2004, Appendix G., p.172, "The [baseline] building
shall be modeled so that it does not shade itself." (P. 178 in
90.1-2007.)

 

Regards,

Bill

 

William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP

Mechanical Engineer

 

134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005

wbishop at pathfinder-ea.com

www.pathfinder-ea.com

P Please strive to live sustainably.

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick
Caton
Sent: Tuesday, March 23, 2010 9:57 AM
To: Wilson, Luke; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] External Shading and Self-Shading

 

Luke,

 

1.       Concur!

2.       First - wow, I never noticed this input... but I'd like to
guess at your intent and have a 90.1 question.  I flipped open my 90.1
2004 & 2007 to find the passage where it says "baseline models shall not
be self-shading..."  and I can't seem to find it =/.  TG3.1, section 5
for building envelope seems to only mention shading projections being
excluded in baseline models.  That said, I'm certain I first picked up
the term "self-shading" somewhere within 90.1... am I incorrect in
thinking/hoping all baseline envelope constructions should have their
"Shading Surface" field set to "No?"

 

~Nick



 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Wilson,
Luke
Sent: Tuesday, March 23, 2010 8:35 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] External Shading and Self-Shading

 

Equest-users,

 

After playing around with my model for a while, I think I can answer my
own questions.

 

1. You can model these surrounding buildings as "Building Shades" in
detailed mode.

2. You can turn off/on whether an external surface is a "Shading
Surface" in the spreadsheet view of Building Shell.

 

Thanks anyway,

Luke Wilson

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Wilson,
Luke
Sent: Monday, March 22, 2010 1:56 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] External Shading and Self-Shading

 

Hello,

I have two questions.

1. If you have a building with other buildings modeled in close
proximity, does equest take into account the shading from the
surrounding buildings?

2. Are equest models self-shaded and if so can you turn this feature
on/off?

 

Thanks in advance,

Luke Wilson


This email and any files transmitted with it are confidential and
intended solely for the addressee. If you are not the named addressee
you should not disseminate, distribute, copy, or alter this email.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100323/f0df4f5f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100323/f0df4f5f/attachment-0002.jpeg>


More information about the Equest-users mailing list