[Equest-users] Complex chiller/heat recovery/heat pump to model question
Matthew Dubrovich
mdubrovich at emcengineers.com
Fri May 7 08:57:57 PDT 2010
Hi Paul,
Though I haven't had the opportunity to use either yet, eQuest has options for both heat recovery chillers and heat pump chillers, correct? You can tie the heat recovery chiller into your hot water loop and it should show both a heating savings and condenser fan savings (eliminating those hand calcs hopefully). The heat pump chillers can be sequenced through Equipment Controls and Load Management to only come on as necessary, after the 165 ton chiller is maxed out. Coupling the heat pumps with your hot water system may be more of a challenge. Good luck.
Matt
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Brooks
Sent: Friday, May 07, 2010 9:26 AM
To: Carol Gardner
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Complex chiller/heat recovery/heat pump to model question
Yes, I did.
Yes, it is an air-cooled Trane Chiller that has total energy recovery. It is a non-US product, made by Trane in Europe.
The concept is that the chiller provids chilled water, and the energy recovery side provides hot water for reheat at VAV boxes when needed.
In addition, there are two heat pumps (reversible chillers as the liturature says)that will pprovide additional capacity to etther the chilled water loop or the hot water loop as needed.
This is for a 110,000 sf high end office building in Uruguay. Uruguay is ASHRAE climate zone 3, similar to the US southeast, primarily Georga/northern Florida.
Links to product information:
Chiller with energy recovery: http://doc.trane-eur.com/marketing/cdtrane.nsf/PdfByName/RLC-PRC026-E4_1205.pdf/$file/RLC-PRC026-E4_1205.pdf
Heat pumps: http://doc.trane-eur.com/Marketing/CdTrane.nsf/PdfByName/CG-PRC015-E4_0708.pdf/$file/CG-PRC015-E4_0708.pdf
I am thinking i will need to do a lot of hand calcs for energy use of the chiller and how much "free" heating water I will get. the hard part is going to be how to account for saving by not running condenser fans. Yes, it will be a challenge to get it through GBCI review, but if the logic is sound, it will not be that hard.
Any suggestions on how to wet up a model in eQuest to minimize amount of hand calculations?
________________________________
From: Carol Gardner <cmg750 at gmail.com>
To: Paul Brooks <equestpaul at yahoo.com>
Cc: equest-users at lists.onebuilding.org
Sent: Fri, May 7, 2010 1:54:56 AM
Subject: Re: [Equest-users] Complex chiller/heat recovery/heat pump to model question
It looks like you stunned everyone into silence, Paul.
So you have 1) an air cooled chiller, 2) heat recovery sending HW to only your reheat coils, 3) 2 air cooled heat pumps that can also provide cool or hot water to circulation loops, 4) french hens, and a partridge in a pear treee...OOPS, its late!
This looks like entropy to me. Try once more to share all of this. I would suggest an itemized list that identifies the equipment type, it's specific use, it's model no. etc. and any comments. Maybe an excel spreadsheet would work best.
Another issue: this project will be neigh on impossible for a LEED reviewer to review, too. That is neither good or bad, it just is.
I will help you as I can, when I can, but I must work for food too. Nobody pays me, yet, to help anyone.
Keep the faith,
Carol
On Thu, May 6, 2010 at 1:47 PM, Paul Brooks <equestpaul at yahoo.com<mailto:equestpaul at yahoo.com>> wrote:
I am modeling a building in Uruguay that has a Trane 165 ton Air cooled chiller, (RTAD 165 SE, not available in US.) In addition to air-cooling, the chiller has a heat exchanger to recover heat for whatever use you want. Obviously the heat recovery means that in the right condisitons the condenser fans will not run as much.
For this application, the heat is to be recovered to provide heating hot water VAV box re-heat coils. In addition to this, there are two air cooled heat pumps (CXAN 214, not available in US) that are available to augment the chiller or the hot wateer loop.
So, my dilemma, is how to model this in eQuest. I am still more or less a novice user. I am in the detail mode, and see that I can do some things with condenser water, but then how do I model the condenser fans? How do I tie in the heat pump loops?
Lastly, this is a LEED model. So, any thoughts on how to get data and then do hand calcs to prove savings are also welcome.
Thanks!
If interestede in seeing info on the equipment, go to Trane-eur.com<http://trane-eur.com/>. information is available in english for these models. Your local trane rep will probably not be able to help.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100507/e60e998b/attachment-0001.htm>
More information about the Equest-users
mailing list