Dennis:
Sorry, not to my knowledge.
ASHRAE 90.1, Appendix G tells you WHAT to include in a model (any model, eQuest, EnergyPlus, TRACE, etc). You will need to play with eQuest to determine HOW it goes into this particular model.
DO make two models, though. An "As Designed" model with everything your building has in it. Then modify the Windows, walls, roof, lighting LPD, HVAC EERs and HSPFs to come up with the Base model. Then compare the two.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: Dennis La Touche <latouche at termoaire.com>
To: equest-users at lists.onebuilding.org
Sent: Fri, May 21, 2010 1:31:15 PM
Subject: [Equest-users] Energy modeling @ ASHRAE 90.1
Hi to all,
I am new using E-Quest.
Is there an online guideline for modeling projects with E-Quest 3.63 according to ASHRAE 90.1 2007 Appendix G?
I’ve been assigned to do the modeling for a LEED v3 registered hotel.
Thank you for your support.
Dennis.
__________ Information from ESET NOD32 Antivirus, version of virus signature database 5034 (20100416) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100521/71ded651/attachment-0001.htm>
More information about the Equest-users
mailing list