[Equest-users] Fire Place
Nick Caton
ncaton at smithboucher.com
Tue May 25 13:23:05 PDT 2010
Hey William,
1. Pull a cutsheet on the fireplace in question to get the input
btu and heating btu incident on the space at full output. If it's not a
commercial gas/electric fireplace with a cutsheet, engineering-judgement
the sucker based on something roughly equivalent.
2. Define a schedule for the fireplace that matches your
definition of "consistently used during cold weather." Consider a
fractional schedule if it's not simply ON/OFF.
3. In detailed mode: Internal loads tab
4. Spreadsheet view, select "Internal Energy Sources"
5. Find the space with the fireplace
6. Define a new load starting with your custom schedule. Fill the
fields in as appropriate - pretty self-explanatory at this point.
Sensible ratio would be your BTU incident on the space over the gross
consumption.
7. Carry around a smug grin coz' now you're the smartest energy
modeler in the room!
Rock on,
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of William
Lopez
Sent: Tuesday, May 25, 2010 2:48 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fire Place
Hi everyone,
I am modeling a cabin log that is heated by electric baseboards and a
fireplace that is consistently used during cold weather.
How can I integrate the fireplace load to the model, what would be the
approach?
Thanks for the help.
William G. Lopez, CEM
Energy Engineer
Buffalo Energy, Inc.
716-677-4899 P
716-677-4722 F
william at buffalo-energy.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100525/1a163caf/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100525/1a163caf/attachment-0001.jpeg>
More information about the Equest-users
mailing list