Scott,
Be sure to check your Heat Input Ratios (HIR) and your Electric Input Ratios (EIR). For a chiller, if your COP is 5.0, your EIR would be 0.2. For a boiler, if your efficiency is 80%, then your HIR is 1.25. If I'm wrong, someone correct me, but I had a huge heat rejection load one time only to find out that my EIR for the chiller was 1.2, instead of 0.2. thanks.
daniel
Daniel I. Deese, EI| CRB Consulting Engineers |
1255 Crescent Green, Suite 350 | Cary, NC 27518 |
P: 919-852-5443 | F: 919-852-5454 | X: 4543
Email: daniel.deese at crbusa.com <mailto:daniel.deese at crbusa.com>
________________________________________________________________________________________
This document may contain confidential information and is intended for use by the addressee only. If you are not
the intended recipient, please do not transmit, copy, disclose, or utilize this communication in any manner. If you
received this message in error, please notify the sender immediately and delete this message.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tomlinson, Scott
Sent: Thursday, May 27, 2010 1:05 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest Users - hydronic question
Dear eQuesters,
Whenever I try to add equipment capacities to anything hydronic, be it a boiler, chiller, or anything else, my energy consumption goes absolutely crazy. Is anyone else experiencing this?
- Thank you,
__________________________________________
Scott Tomlinson, PE, LEED-AP
Mechanical
Symmes Maini & McKee Associates, Inc.
1000 Massachusetts Avenue, Cambridge, MA 02138
t: 617.520.9438
f: 617.354.5758
stomlinson at smma.com
www.smma.com <http://www.smma.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100527/e9ffb6e7/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14792 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100527/e9ffb6e7/attachment-0001.jpeg>
More information about the Equest-users
mailing list