[Equest-users] Chiller Curves (oh boy!)

Paul Diglio paul.diglio at sbcglobal.net
Wed Nov 3 11:18:13 PDT 2010


John:

In my opinion one needs to get the chiller modeled by the factory as the 
catalogs do not contain nearly enough information.

See attached spreadsheet.  The top portion was provided by Trane.  It models 
this chiller at Standard, Maximum and Minimum condenser water flows.  I 
performed the calculations in the red border.

I needed to model this in Excel for a utility incentive.  I was implementing 
variable condenser water flow.  The kW/Ton increases using a variable flow 
sequence.

My total kWh savings for varying the speed of the condenser pumps was 
approximately 250,000.  The chiller consumed approximately 50,000 kWh more with 
minimum condenser water flow.

Trane modeled this project several times for me, they had a self-interest 
because I was contracting them to perform some board upgrades as part of the 
energy efficiency project.

Paul Diglio




________________________________
From: Carol Gardner <cmg750 at gmail.com>
To: John T. Forester <JohnTF at bvhis.com>
Cc: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Wed, November 3, 2010 1:54:35 PM
Subject: Re: [Equest-users] Chiller Curves (oh boy!)

I agree with you, John, but have a couple of other thoughts to add. The first is 
I have not met a mechanical engineer that does not select a chiller that is 
capable of supplying all loads. In fact, they generally oversize a bit to 
accommodate possible future loads. The only piece of equipment I have ever seen 
selected at over 100% was a VRV system and that is because they actually work 
better at 120% loading. The second is that you can generally get a catalog from 
a manufacturer to have on your shelf that has technical information like how the 
chiller unloads based on temperatures and what the efficiency is at part load so 
you can look up the chiller you need info for and not need to bother the ME or 
the vendor. If you can't get/don't want a hard copy, most of this info is on 
line, just look for technical specifications.

Best,

Carol


On Wed, Nov 3, 2010 at 9:48 AM, John T. Forester <JohnTF at bvhis.com> wrote:

Nick,
> 
>I think you’re on the right track.  Below are some of my thoughts on your 
>conclusions.  I hope the modeling community will set me straight if I’m wrong 
>here.
> 
>	1. Getting      multiple performance runs from vendors that show part-load 
>performance      independent of the CW and CHW temps can often be challenging.  
>Adding the “maximum      capability” task to that for each of the conditions 
>requires a pretty      detailed understanding of the selection software.  I’d 
>say if you can get      PLR data for 3-4 different CHW temps while holding the 
>CW temps constant      at 85, 75, 65 (and sometimes lower) – you’re ahead of 
>most modelers.  Working      with the Mechanical Design Engineer and the vendor 
>together has been      successful for me in the past.
>	2. Defining      the chiller capabilities at the “maximum” may only come into 
>play if you      expect your model to overload the chiller above the specified 
>design      capacity (I’m thinking building additions or process loads). At this      
>point, this data (or knowing what the default eQuest curves do in that      
>range) would be useful.  Depending on your project, the time spent on developing      
>curves for PLR >1.0 may not be justified.
>	3. If      you don’t have “max” data and don’t want eQuest to assume 
>performance at a      part-load ratio >1.0, you can set the DESIGN-PLR to 1.0.
>	4. Either      way, you want your curves to be normalized at whatever condition 
>you      specify (Design or Rated) and you want to enter those values on the 
>Basic Specifications      tab.
> 
>John
> 
>John T.  Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated 
>Services I617.658.9008 tel I617.244.3753 fax IOne Gateway Center Suite 506, 
>Newton MA 02458 I www.bvhis.com I Hartford ● New Haven ● Boston
>size=2 width="100%" align=center tabindex=-1> 
>From:Nick Caton [mailto:ncaton at smithboucher.com] 
>Sent: Wednesday, November 03, 2010 12:06 PM
>To: John  T. Forester; equest-users at lists.onebuilding.org
>
>Subject: RE: [Equest-users] Chiller Curves (oh boy!) 
> 
>John,
> 
>The design/max ratio is exactly what I’m discussing below when I say “DESIGN-PLR 
>ratio,” so we’re definitely in the same ballpark =).
> 
>I’d like to apply/paraphrase your advice to a few conditions to be sure I’m 
>getting it correctly:  
>
>-          If we create all 3 custom curves, and normalize each to a point at 
>maximum (not design) capacity, then the design-to-max ratio (DESIGN-PLR) should 
>be set to 1.00.
>-          If we create only the part load efficiency curve (EIR-FPLR or 
>EIR-FPLR&dT), and wish to use the library defaults for EIR-FT and CAP-FT, then 
>we should normalize this curve’s data points to ARI conditions (as that’s what 
>the library curves are normalized to, per James’s email – I think I’ve read this 
>somewhere also), specify an ARI  capacity, EIR and conditions on the basic 
>specifications tab, and enter a DESIGN-PLR of [ARI capacity/maximum capacity 
>(for the same conditions)].
>-          If we create all 3 custom curves, and try to normalize each to either 
>ARI or design conditions, then we should specify capacity, EIR, CHWT, CWT and 
>condenser GPM corresponding to either the ARI or design conditions of that 
>normalizing point.  In that case, we also specify a DESIGN-PLR using either the 
>ARI or design capacity divided by the maximum capacity for the same conditions.
> 
>Profound (to me) Conclusion:  In No instance should we Ever attempt creating 
>custom curves and NOT have at least one run from our manufacturer telling us 
>what the maximum (not design) capacity is for the normalizing point.  This 
>conclusion would only apply to centrifugal chillers only.
> 
>Does this all sound right?
> 
>~Nick
> 
> 
>James, 
> 
>Yeah, if all the part load data you received held the same CHWT and CWT equal, 
>you might be able to make your part-load curve if it could have been a quadratic 
>EIR-FPLR curve (like a reciprocating chiller), but not a bi-quadratic 
>EIR-FPLR&dT (as with my centrifugal VSD chiller).  You definitely could not 
>approach generating custom EIR-FT or CAP-FT curves without varying condenser and 
>chilled water temps.  That exact issue happened to me the first few times I 
>tried to reign my chiller reps in =).  
>
> 
>This time, I convinced my rep to give me multiple part load runs holding the 
>CHWT constant and varying the CWT incrementally.  This let me build the 
>bi-quadratic EIR-FPLR&dT curve as I had at least three different dT’s 
>represented in my part load data points.  I plotted the 3D curve in excel to 
>check my work and darned if the generated coefficients seem to be really 
>accurate =)!   It’s currently looking like a bittersweet revelation however – 
>the library curve for a water-cooled centrifugal VSD chiller (see attached 
>visualization) seems a LOT more generous (more efficient) at low part loads than 
>the one I’ve generated which matches my rep’s data…  I might share a visual of 
>my custom curve for comparison once I’m dead-sure it’s accurate – I’m trying to 
>clarify a few things with my rep right now.
> 
>~Nick
> 
> 
>NICK CATON, E.I.T.
>PROJECT ENGINEER
>25501 west valley parkway
>olatheks 66061
>direct 913 344.0036
>fax 913 345.0617
>Check out our new web-site @ www.smithboucher.com
> 
>From:John T. Forester [mailto:JohnTF at BVHis.com] 
>Sent: Wednesday, November 03, 2010 10:29 AM
>To: Nick Caton; equest-users at lists.onebuilding.org
>Subject: RE: [Equest-users] Chiller Curves (oh boy!)
> 
>Nick,
> 
>When defining a centrifugal chiller in eQuest, one of the items on the Basic 
>Specifications tab under the Design vs. Rated Conditions is a Design/Max Cap 
>ratio.  By default, this is 92% for a water cooled unit.  I believe this gets at 
>the discussion in the help pages that talks about maximum capacity versus design 
>capacity and how the chiller vendor will spec a piece of equipment.  Typically, 
>vendors don’t often get asked (or provide) what the “Maximum” capacity of a 
>spec’d unit is.  Therefore the performance data that they provide are at “design 
>conditions.”
> 
>If you change the chiller type to a reciprocating chiller, this “Design/Max Cap” 
>ratio is disabled and the default specified condition changes from “Design 
>Conditions” to “Rated Conditions.”  This suggests that there is little “extra” 
>capacity when a selection is done for that type of chiller.
> 
>If you do get “maximum capacity” data and create curves from that data, you will 
>want to change the Design/Max Cap ratio to 1.0 so eQuest knows that there isn’t 
>any spare capacity at the chiller.  Also if the data points you are using to 
>normalize your curves are different than the design conditions for your energy 
>model, you will want to change the “Chiller Specified at” value to “Rated 
>Conditions” and enter the rated conditions for CHW temp, CW temp and CW gpm/ton 
>to match your normalized curves.
> 
>Hope this helps,
> 
>John
> 
>John T.  Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated 
>Services I617.658.9008 tel I617.244.3753 fax IOne Gateway Center Suite 506, 
>Newton MA 02458 I www.bvhis.com I Hartford ● New Haven ● Boston
><hr size=2 width="100%" align=center tabindex=-1> 
>From:equest-users-bounces at lists.onebuilding.org 
>[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
>Sent: Wednesday, November 03, 2010 11:03 AM
>To: Carol Gardner; equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] Chiller Curves (oh boy!)
> 
>Thanks for the response Carol!
> 
>That 120% load case is what I’m getting at – let me try to explain a little 
>further:
> 
>In the DOE2 help files, the vocabulary for centrifugal chillers is “design 
>capacity” and “maximum capacity,” where “design” means the capacity at the rated 
>or designed conditions (at which you define / specify your chiller), and 
>“maximum” means the capacity the chiller is really capable of under the same 
>conditions if it runs balls-out (maximum power to the refrigerant drive).
> 
>The help file excerpt I copied below with the red line is pretty explicitly 
>telling us to normalize the part load values to the maximum capacity for 
>centrifugal chillers.  I’ve highlighted a second line for clarity.  The EDR 
>guidelines I linked below are saying you can instead normalize to the design 
>capacity for the EIR-PLR curve if that’s all your field measurements or 
>manufacturer rep can provide.
> 
>I’m asking – are both approaches right?  
> 
>My first and second questions are kinda tied together… How would choosing to 
>normalize to either the maximum or design conditions affect how we should handle 
>the DESIGN-PLR ratio, if at all?
> 
> 
>~Nick.
> 
> 
>NICK CATON, E.I.T.
>PROJECT ENGINEER
>25501 west valley parkway
>olatheks 66061
>direct 913 344.0036
>fax 913 345.0617
>Check out our new web-site @ www.smithboucher.com
> 
>From:Carol Gardner [mailto:cmg750 at gmail.com] 
>Sent: Tuesday, November 02, 2010 10:04 PM
>To: Nick Caton
>Cc: equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] Chiller Curves (oh boy!)
> 
>Let me take a crack at this. If by design capacity you mean the chiller running 
>at 100% load, you would create the curve(s) by normalizing around your ARI 
>design conditions i.e. the PLR curve would be 1.0 at this point, call it ARI Cap 
>and the other points would be 90% Cap/ARI Cap, 80% Cap/ARI Cap, etc. The same 
>would go for your temp curves. If, however, your chiller is operating at 120%, 
>or some such other level, I would normalize the curve around the ARI design 
>conditions of the chiller at 120%. I had to do this for a VRV hp that was 
>selected at the 120% design condition.
>
>I find this from the DOE2 manual the most helpful:
>  
>Volume 2: Dictionary> HVAC Components> CURVE-FIT> INPUT-TYPE = DATA
>INDEPENDENT-2
>Used for all curves having two independent variables. A list of up to twenty 
>values of the second independent variable. The number of values should be the 
>same as for DEPENDENT.
>Example 1: defining a curve by inputting a set of data points.
>A packaged system (PZS) has cooling performance significantly different from 
>that used in the default  model. The manufacturer lists the data shown in Table 
>46, for cooling capacity, at 2000 cfm design air flow rate, as a function of 
>outside dry-bulb temperature and entering wet-bulb temperature.
>Table 46  Cooling capacity (kBtu/hr) vs. temperature
>Outside
>Dry-bulb Entering   Wet-bulb 
>72F 67F 62F 
>85F 69 65 60 
>95F 68 63 (ARI) 57 
>105F 65 60 53 
>115F 62 55 49 
> 
>In this example the independent variables are the entering wet-bulb temperature 
>and the outside dry-bulb temperature. Because there are two independent 
>variables and they have units of temperature, we input a curve of TYPE 
>BI-QUADRATIC-T using the given data points. The dependent variable is not the 
>cooling capacity listed in the table but rather the cooling capacity divided by 
>the cooling capacity at the ARI rating point (95 F outside dry-bulb and 67 F 
>entering wet-bulb). In other words, the capacities should be normalized to the 
>ARI rating point., as shown in Table 47
>Table 47  Normalized capacity vs. temperature
>Outside
>Dry-bulb Entering   Wet-bulb 
>72F 67F 62F 
>85F 1.095 1.032 0.952 
>95F 1.079 1.0 (ARI) 0.905 
>105F 1.032 0.952 0.841 
>115F 0.984 0.873 0.778 
> 
>The CURVE-FIT input will look like the following:
>CAP-CURVE-1 = CURVE-FIT
>TYPE               = BI-QUADRATIC-T
>INPUT-TYPE         = DATA
>DEPENDENT          = (1.000,1.079,0.905,1.032,0.952,0.841,
>                      0.984,0.873,0.778,1.095,1.032,0.952) ..
>IN-TEMP1           = (   67,   72,   62,   72,   67,   62,
>                         72,   67,   62,   72,   67,   62) ..
>IN-TEMP2           = (   95,   95,   95,  105,  105,  105,
>                        115,  115,  115,   85    85,   85) ..
>Example 2: Defining a curve by inputting coefficients
>We want a furnace to have a constant efficiency as a function of part load. To 
>do this we must replace the default FURNACE-HIR-FPLR with a curve that will give 
>a constant efficiency. The curve TYPE is QUADRATIC in the part load ratio (PLR). 
>PLR correction curves are always multiplied by the unit capacity, not the load, 
>to obtain the energy (fuel or electricity) use. Thus the curve we want is: 0.0 + 
>1.0*PLR + 0.0*PLR*PLR. The input will look like:
>New-Furnace-HIR-fPLR = CURVE-FIT
>TYPE               = QUADRATIC
>INPUT-TYPE         = COEFFICIENTS
>COEFFICIENTS       = (0.0,1.0,0.0) ..
>Then in the SYSTEM command we include:
>   FURNACE-HIR-FPLR = New-Furnace-HIR-fPLR
> 
>On Tue, Nov 2, 2010 at 3:21 PM, Nick Caton <ncaton at smithboucher.com> wrote:
>Hi everyone!
> 
>I think I have finally wrapped my mind completely around custom chiller 
>performance curves for a centrifugal VSD chiller.  I’ve got a few specific 
>questions now that I’m on the other side of the fence:
> 
>1.       Is it necessary for the data points of a part load efficiency curve 
>(EIR-FPLR&dT in my case) to originate from data with a 1.0 (100%) PLR ratio 
>corresponding to a maximum vs. a design load capacity?  From what I gather in 
>the EDR reference (re: “Method 2” on PDF page 32/65), this curve can be 
>generated using part-load readings assuming a design capacity at the 100% 
>loading mark… but the DOE2 help entry for “EIR-FPLR” seems to suggest otherwise 
>(copied below – see highlighted line).
>2.       If the above part load efficiency curve is created based on data where 
>the 100% loading point corresponds to the maximum (not design) capacity, should 
>“DESIGN-PLR” (the ratio of design to maximum capacity) be set to 1.00 and the 
>capacity of the chiller be specified at its maximum (not design) for the 
>design/rated conditions?  As I write this question it sounds like I’m chasing my 
>tail – someone straighten me out =)!
>3.       When you veterans finish a project with sets of custom performance 
>curves, do you have any suggestions for a naming scheme for future 
>reference/re-use?  I’m currently thinking to keep the curves grouped in an .inp 
>snippet I for importing along with an equipment cutsheet… but I’m certain I’ll 
>forget the all the details as quickly as humanly possible when this project is 
>behind me…
> 
> ~Nick
> 
> 
>NICK CATON, E.I.T.
>PROJECT ENGINEER
>25501 west valley parkway
>olatheks 66061
>direct 913 344.0036
>fax 913 345.0617
>Check out our new web-site @ www.smithboucher.com
>EIR-FPLR
>Takes the U-name of a curve that adjusts the electric input ratio as a function 
>of
>· The part load ratio (PLR) –  The PLR is defined as the ratio of the hourly 
>load to the hourly capacity;  Load / Caphour
>· The evaporator/condenser dT -  The temperature differential between the 
>condenser and leaving chilled-water. The  meaning of the condenser temperature 
>varies according to condenser type. 
>
>For most chillers, the dT has a relatively small effect on part-load 
>performance. However, for variable-speed centrifugal chillers, the effect of dT 
>is as important as the PLR.  This is because the pressure rise across the 
>impeller is proportional to the square of the impeller’s speed. Unless some form 
>on condenser temperature relief is employed to reduce the temperature (and 
>pressure) differential across the chiller at part load, the performance of a 
>variable-speed chiller may not be significantly different than that of a 
>constant-speed chiller.
>To model power consumption as a function of the PLR only, use a CURVE-FIT of 
>TYPE = QUADRATIC or CUBIC.  To model as a function of both PLR and dT, use a 
>BI-QUADRATIC-RATIO&DT curve. The curve must be normalized to 1.0 at full load 
>and the rated temperature differential. 
>
>Note that, for centrifugal chillers, ‘full load’ is defined as the ‘maximum 
>capacity’, not the ‘design capacity’. Refer to the DESIGN-PLR keyword for more 
>information.
> 
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>-- 
>Carol Gardner PE
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to 
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101103/24734c75/attachment-0001.htm>