[Equest-users] auxilliary heat and desiccant wheel

Nick Caton ncaton at smithboucher.com
Fri Nov 5 12:05:12 PDT 2010


Hi Alan!

 

1.       "auxilliary strip heat:" Not totally sure what specifically
you're talking about (vocabulary disconnect probably), but I think
you'll find what you're looking for under the "supplemental heat/defrost
tab" in detailed mode.

2.       Look in the same place first... alternatively you may be able
to specify dual fuel as a pre-heat option

3.       Easiest approach, for projects large and small, generally is
to:

a.       Go to the airside system(s) served by the OA unit, 

b.      Enable/define energy recovery inputs (including wheel
properties), and 

c.       Proportion out the delivered flow rates and fan/process
energies of your OA unit between the served systems

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alan
Crittendon
Sent: Friday, November 05, 2010 9:46 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] auxilliary heat and desiccant wheel

 

 

How do I factory in the auxilliary strip heat or use a dual fuel heat
option for packaged heat pumps?  Also how do I put in a desiccant wheel
for an outside air unit?

 

Alan Crittendon, PE, LEED AP
DW Collier Engineering, Inc.

720 Broadway St.

Suite 100

South Fulton, TN 38257
(p) 731-479-2115
(f) 731-479-8018 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/744fff33/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/744fff33/attachment-0001.jpeg>


More information about the Equest-users mailing list