[Equest-users] Baseline Chilled Water Loop

John T. Forester JohnTF at BVHis.com
Tue Nov 16 05:41:04 PST 2010


Fellow Modelers,

I’ve received a comment regarding my response last week on how to model CHW pumps for App. G.  Specifically, item 7 (see below) and how the 22 W/gpm is defined for a primary secondary configuration.  Section G3.1.3.10  can be interpreted (at least) two different ways.

First, Section G3.1.3.10 Chilled-Water Pumps (Systems 7 and 8)
“The baseline design pump power shall be 22 W/gpm.  Chilled-water systems with a cooling capacity of 300 tons or more shall be modeled as primary/secondary systems with variable-speed drives on the secondary pumping loop.  Chilled-water pumps in systems serving less than 300 tons cooling capacity shall be modeled as primary/secondary systems with secondary pump riding the pump curve.”

The question:
Should each primary and secondary pump be sized for 22 W/gpm OR should this “design pump power” be divided up (in some way) between the primary and secondary pumps?

Position A:
If the 22 W/gpm should be the TOTAL pumping power, there is no guidance on how to divvy up this requirement and the constant volume primary pumps could be sized for 20 W/gpm and the secondary (VSD or riding pump curve) can be allotted 2 W/gpm.  This would maximize the pump energy in the baseline model.

Position B:
Sizing each primary pump and secondary pump to 22 W/gpm will over-estimate the baseline pump energy (VSD or riding pump curve) and this is not the intent of 90.1.  The “design pump power” of 22 W/gpm is the same requirement as Section 11 (ECB method) just with a different pumping configuration.

How do you interpret (and model) 90.1 App. G chilled-water pump power requirement of 22 W/gpm?  (Your interpretation doesn’t necessarily have to be one of the positions above.)

Thanks,

John


John T. Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated Services I 617.658.9008 tel I 617.244.3753 fax I One Gateway Center Suite 506, Newton MA 02458 I www.bvhis.com<http://www.bvhis.com> I Hartford ● New Haven ● Boston
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John T. Forester
Sent: Friday, November 12, 2010 5:47 PM
To: 'Smith, Michael'
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Chilled Water Loop

Hi Michael,

I think I can answer your App G question.

First, in the context of 90.1, “variable flow” does not necessarily mean variable speed.  It just means riding the pump curve with a bypass to minimize pumping pressure drops through the loop during part-load operation.

App. G Chilled Water Modeling <=300 tons

1.       Create a chilled water circulation loop and name it something like “Pri CHW Loop.”

2.       Create another chilled water circulation loop and name it something like “Sec CHW Loop.”

a.       Change the Loop Sub-type of this loop to Secondary and choose “Pri CHW Loop” as the primary loop.

3.       Create a circulation pump and name it something like “Sec CHW Pump.”

a.       Set this pump as variable speed.  I believe you are allowed to set the minimum speed to 50% for App. G. (someone here on the list can correct me on this if I’m wrong).

b.      By default, the valve on this loop is three-way and will circulate water directly back to the primary loop as long as there are two-way valves at your terminal units (AHU coils, FCUs, etc).

c.       Attach this pump to the Sec CHW Loop.

d.      Change the loop head sensor location to “at coils.”

4.       Create a condenser water loop and CW pump and attach the pump to the loop.

a.       Also create an open tower heat rejection device and attach it to your condenser water loop.

5.       Create 1 primary chilled water pump per chiller.  They won’t be attached to anything yet and will be at the bottom of the component tree.

a.       The default for a pump is “One-Speed.”  This is fine and the pump will act as a constant volume pump with the three-way valve on the secondary loop.

6.       Create a water-cooled chiller and choose the “Pri CHW Loop 1” and “water-cooled.”

a.       Since there is no pump attached to the primary loop, you will be required to select a pump for the chiller.

b.      You will also be required to select the Condenser water loop

7.       Now what you have to do is size your pumps so the total pump energy is 22 W/pm.  You will want to do something like 4-5 W/gpm for each primary pump and use the remaining for the secondary pump.

This system is primary/secondary with constant flow through each chiller and variable speed/variable flow through the secondary loop.  Since each chiller has a pump directly attached to it, each primary pump will automatically cycle on and off with the chillers.



John T. Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated Services I 617.658.9008 tel I 617.244.3753 fax I One Gateway Center Suite 506, Newton MA 02458 I www.bvhis.com<http://www.bvhis.com> I Hartford ● New Haven ● Boston
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Smith, Michael
Sent: Friday, November 12, 2010 3:55 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Chilled Water Loop

Everyone,

I have a question regarding the baseline chilled water loop.

ASHRAE 90.1 2007 Section G3.1.3.10 states that for large chilled water systems serving baseline systems 7 and 8 that are greater than 300 tons the loop “shall be modeled as primary/secondary with variable speed drives on the secondary pumping loop.”

The following section, G3.1.3.11 further goes on to say that “each chiller shall be modeled with separate…chilled water pumps interlocked to operate with the associated chiller.”
As clarification, does this mean three sets of pumps are required, or just two? Are the “primary” loop pumps specified as the chiller pumps?
Two reasons why I am confused. Firstly, the Chapter 11 baseline chilled water loop is supposed to be simulated as primary-only variable flow, but still has the similar requirement for interlocked chiller pumps. That would be two sets of pumps. Adding a “secondary” loop actually adds a third set of pumps.
The second reason why I am confused is that the Simulation Guidebook<http://www.energydesignresources.com/Portals/0/documents/DesignGuidelines/EDR_DesignGuidelines_%20HVAC_Simulation.pdf> prepared for Pacific Gas and Electric (same affiliation as CoolTools) has a visual of how to simulate “primary/secondary” loops on page 52, but they do not include chiller pumps in their image of the eQUEST component tree.
I can’t understand why three sets of pumps would be required. I supposed a follow up question may be if the 22 watts/gpm is inclusive of all three sets of pumps. Hopefully someone can clarify! I appreciate your help.


Michael J. Smith, EIT, LEED® AP
WSP ▪ FLACK + KURTZ
512 7th Ave., New York, NY 10018
Direct: 212.951.2671| Main: 212.532.9600
www.wspfk.com<http://www.wspfk.com/>


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101116/cdc73b8f/attachment-0001.htm>


More information about the Equest-users mailing list