[Equest-users] design flow input vs. SV-A supply flow reporting

Carol Gardner cmg750 at gmail.com
Fri Oct 8 07:33:46 PDT 2010


Not stupid at all, If you have your altitude set to anything but 0 eQUEST
will adjust your cfm accordingly. I always go in and set it manually to
zero. I think it reads what it is off the weather file.

Carol

On Fri, Oct 8, 2010 at 6:54 AM, Christian Stalberg <
cstalberg at naturalintelligence.us> wrote:

>  They say no question is a stupid question.
>
> Why is my zone level supply flow cfm reported value in the SV-A report
> higher than my overall design flow (ASSIGNED-FLOW) value? The
> system sizing ratio is set at 1.00 (default).
>
> Thanks in advance.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101008/1ae9c1bd/attachment-0001.htm>


More information about the Equest-users mailing list