[Equest-users] (no subject)

Eddie Corwin ecorwin at altanova-energy.com
Tue Oct 19 08:27:36 PDT 2010


You can not make a "Doughnut" zone.  you will need to separate the perimeter 
zone into two or more zones.  Using the "Core/Shell Zoning pattern that is 
available in the wizard works well.  






________________________________
From: Erik Weiss <ew0187 at gmail.com>
To: equest-users at lists.onebuilding.org
Sent: Tue, October 19, 2010 11:22:08 AM
Subject: [Equest-users] (no subject)

I am creating a 20 floor building and the core is defined. i am trying to create 
the zones within the core and the large single zone surrounding the core. I am 
unable to create 1 single zone surrounding the core because the wizard does not 
allow you to select the same vertex twice in a single zone. Is there anyway 
around this 

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/7a49ace4/attachment-0001.htm>


More information about the Equest-users mailing list