[Equest-users] Equest v3.64 - Plenum and Zones
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Sep 2 08:37:30 PDT 2010
Mike,
The eQUEST wizard will create plenums based on the inputs for systems.
For example, if you use the Schematic Design Wizard and select a VAV
system, you will get one plenum per floor. If you select Packaged Single
Zone you will get one plenum per zone. If you use the Design Development
Wizard, you have the option of selecting System per Floor or System per
Zone, which will create the plenums accordingly.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike
Schaefer
Sent: Thursday, September 02, 2010 8:49 AM
To: EQuest
Subject: [Equest-users] Equest v3.64 - Plenum and Zones
After setting up an overall buidling footprint and then the zones eQuest
creates a large plenum that encompasses all zones. How can I divide this
plenum to correlate to it's respective zone? When I have mutlipy systems
I'm forced to assign the plenum return to one system instead of the
related zones.
I'd appreciate any input. Thanks,
Michael Schaefer - P.E., LEED(r) AP
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100902/8ae464ca/attachment-0001.htm>
More information about the Equest-users
mailing list