[Equest-users] Review Requested
Sami, Vikram
Vikram.Sami at perkinswill.com
Thu Sep 9 12:54:52 PDT 2010
Just to add to what Eddie said - you will spec OA from only when you are borrowing outside air from another system (Like with a DOAS). I've actually never seen this before (where you specify OA-From as the same system). What its probably doing is taking your return air as OA (at around 78) and cooling it (and taking moisture out of it).
I would have thought it would give you an error.
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eddie Corwin
Sent: Thursday, September 09, 2010 3:26 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Review Requested
In both of your HVAC systems you have "Outdoor Air From System" object specified. In most cases, you will want to leave this object blank. The only time would want to use that object if, for example, you were taking the return air from one system, and using it in another, separate, system. I am pretty sure that in your case, especially in the labs, all of the air will be coming from the outside, or will be recirculated within the same system.
If you reset those values to their default you get much better cooling results, but you also get heating in the summer, which is another issue you need to look at in more detail. The "Outdoor Air From System" object is found in your HVAC system --> Outdoor Air --> Outdoor Air and Economizer
-Eddie
________________________________
From: "equest-users-request at lists.onebuilding.org" <equest-users-request at lists.onebuilding.org>
To: equest-users at lists.onebuilding.org
Sent: Thu, September 9, 2010 3:03:35 PM
Subject: Equest-users Digest, Vol 30, Issue 13
Note: Forwarded message is attached.
Send Equest-users mailing list submissions to
equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
or, via email, send a message with subject or body 'help' to
equest-users-request at lists.onebuilding.org<mailto:equest-users-request at lists.onebuilding.org>
You can reach the person managing the list at
equest-users-owner at lists.onebuilding.org<mailto:equest-users-owner at lists.onebuilding.org>
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Equest-users digest..."
Today's Topics:
1. LEED compliance new version of eQuest (Peter Hillermann)
2. LEED compliance new version of eQuest (Peter Hillermann)
3. Re: Review Requested (Umesh Atre)
4. Re: Infrared Heaters (Peter Hillermann)
5. Re: Review Requested (Paul Diglio)
6. Re: Reduction of window area in detail mode! (Arunabha Sau)
7. Re: Infrared Heaters (Peter Hillermann)
8. Re: Infrared Heaters (Nick Caton)
9. Re: Infrared Heaters (Peter Hillermann)
10. Re: Review Requested (Umesh Atre)
11. Re: Floor Slab F-factor (Jeremy Poling)
12. Re: Infrared Heaters (Charles Land)
_______________________________________________
Equest-users mailing list
Equest-users at lists.onebuilding.org<mailto:Equest-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/1c911dca/attachment-0001.htm>
More information about the Equest-users
mailing list