[Equest-users] Baseline HVAC Single Zone Furnace Operation.

Mark Darrall MDarrall at a2so4.com
Mon Apr 4 04:24:50 PDT 2011


Hi!

G3.1.2.1 is pretty clear that for the baseline model you're supposed to use the minimum equipment efficiencies shown in Section 6.4. In other words, the single zone gas furnace you reference would be baseline-modeled per Table 6.8.1E, so a small gas furnace (<225 MBH) would be 78% AFUE.

So your equipment EEM in your design case would be the 94% furnace.

The only way I know this is because I'm working on a building with 6 of these little guys.

Good luck!

MARK DARRALL, AIA, LEED AP BD+C, NCARB
Senior Project Manager

[cid:image001.jpg at 01CBF299.08F149E0]

DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN

A2SO4 Architecture, LLC
Union Station
300 South Meridian Street / 250
Indianapolis, Indiana 46225
TEL  317 388 8850
FAX  317 280 0692
MOB 765 749 0841
www.a2so4.com

Please consider the environment before printing this e-mail.

CONFIDENTIALITY NOTICE: This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient, you may not review, copy or distribute this message. If you have received this email in error, please notify the sender immediately and delete the original message. Neither the sender nor the company for which he or she works accepts any liability for any damage caused by any virus transmitted by this email.

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Carol Gardner
Sent: Wednesday, March 30, 2011 8:59 PM
To: Kathryn Kerns
Cc: equest-users at lists.onebuilding.org; Steve Butros
Subject: Re: [Equest-users] Baseline HVAC Single Zone Furnace Operation.

Sorry I accidentally hit the send button.

I was saying, my take on modeling systems that Appendix G and the rest of Standard 90 don't supply specific requirements for is to make them reasonably inefficient. I say reasonably because it has to be within reason, so that you can't be accused of gaming the system. In this case you have further justification for using the modulating baseline as you truly don't have any information about staging,

Cheers,

Carol
On Wed, Mar 30, 2011 at 5:53 PM, Carol Gardner <cmg750 at gmail.com<mailto:cmg750 at gmail.com>> wrote:
Hi Kathryn,

Thanks for sharing your solution to the Georgia project. It sounds like a really good idea, simple yet effective. It's funny I don't think I would have thought of using 2 DOAS units, but why not?

WRT to the furnace. My ta
On Wed, Mar 30, 2011 at 1:59 PM, Kathryn Kerns <kathryn.kerns at bceengineers.com<mailto:kathryn.kerns at bceengineers.com>> wrote:
Everyone, I may have asked this before, but has anybody run across a section of ASHRAE 90.1 or LEED describing the operation of a baseline furnace in a PSZ unit? Do we assume the heating modulates or does it stage? And if it stages, how many stages? I have been modeling baseline furnace heating as modulating since that is what naturally appears in eQuest, but I wonder. I know in reality that a lot of small furnace heaters cycle to maintain space heat.

Also, I promised I would share results of my struggle to model dehumidification for a project in Georgia. I was sort of successful, I think. What I ended up doing was attaching 2 DOAS in series. The first DOAS had a cooling only heat pump and the second unit had heating only heat pump. The first unit handled the outside air and passed space/return air to the second DOAS.  The second unit supplied space/return air to the terminal units. This way I got to define set points for the first DOAS cooling supply temperature (space/return temperature) and the second DOAS heating supply (space/return temperature). The amount of energy consumed and size of each unit was adjusted to approximate a horseshoe dehumidification unit. It seemed to work.




Kathryn Kerns

Systems Specialist

BCE Engineers, Inc.

| Ph: 253.922.0446<tel:253.922.0446> | Fx: 253.922.0896<tel:253.922.0896> |



_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



--
Carol Gardner PE



--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110404/c9685ea3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2061 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110404/c9685ea3/attachment.jpg>


More information about the Equest-users mailing list