[Equest-users] Low emissivity fabric in ice rink

Keith Swartz kswartz at ecw.org
Sun Apr 3 20:31:23 PDT 2011


Adam,

Ceiling emissivity can be entered (along with a lot of other ice rink data) in the detailed interface.

1. Click the "Air-Side HVAC" button near the top of the screen.
2. In the comonent tree on the left, select the zone that has the ice rink.
3. Click "Spreadsheet" near the top of the screen.
4. Select "Ice Skating Rinks" for Display Mode. Scroll horizonatally about half way to find ceiling emissivity.
________________________________
Keith Swartz, P.E., LEED AP

Energy Engineer / Senior Project Manager
Energy Center of Wisconsin
455 Science Drive, Suite 200, Madison, WI 53711
Phone: 608.238.8276 x123
Fax: 608.238.0523

The Buildings Team
Design decisions through energy, economics and emissions analysis.
www.ecw.org/Buildings<http://www.ecw.org/Buildings>

Energy Center University
Your gateway to sustainable design training and online education programs.
www.ecw.org/university/<http://www.ecw.org/university/>
________________________________
From: atowell at cxegroup.com [atowell at cxegroup.com]
Sent: Friday, April 01, 2011 3:22 PM
To: eQuest List (equest-users at lists.onebuilding.org)
Subject: [Equest-users] Low emissivity fabric in ice rink

Does anyone know how I could go about describing a low-emissivity fabric for an ice rink ceiling?

Adam Towell
CxE Group, LLC
618-659-9461

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110403/3c952486/attachment-0001.htm>


More information about the Equest-users mailing list