Regarding the fan power.  If we assume that both fans and fan motors have
the same efficiency and the units are constant volume, then you will adjust
the static pressure of your fan coil units by the current flow over the new
flow when you add the outside air.



i.e. if you have two FCU’s current supplying 2000 cfm and you have a 1000
cfm outside air unit delivering 500 cfm to each FCU, then your new FCU
supply air rate will be 2500 cfm.  You will build your DOAS as is designed
and you will bump up your FCU airflow quantity to the total of the design
and the DOAS supply to that space/zone/system.  You will then reduce your
static pressure for the FCU by 2000/2500 or 80% of what it is designed at,
if the design total static is 4 inches then your new static will be 3.2
inches.  This will eliminate any increase in fan power that you may see to
the increased flow.  (If you have ten FCUs at 2000 cfm and a DOAS at 2000
cfm, your numbers with the DOAS would be, DOAS as designed, 2200 cfm for
each FCU, and a new total static pressure at 2000/2200 of design or 90.9% of
design static).





As for the process, you say isenthalpic, so to me that means that the air is
delivered off of the evaporator coil after the refrigerant goes through an
expansion valve?

Or could you please tell us what N, L, O, S, and W stand for, and what the
axes of this chart are, (temperature and entropy?)  It doesn’t look like a
psychrometric chart.







Joe Fleming, E.I., LEED AP BD+C, BEMP



From: tiejun hu [mailto:hutiejun1223 at 126.com]
Sent: Thursday, April 14, 2011 9:40 AM
To: Joe Fleming
Cc: 'equest-users'
Subject: Re:RE: [Equest-users] FC+DOAS






At 2011-04-14 21:03:47,"Joe Fleming" <joe at thespinnakergroupinc.com> wrote:



Search DOAS in the user archives and you will find a bunch of discussions on
this topic.



First you need to be in detailed mode, for some reason the DOE engine (maybe
just eQuest), doesn’t have the skills to make a dedicated outdoor air
system as a drop down selection.



Next, what is the supply air temperature entering the zones from the DOAS?
Cold?  Room temperature? Hot?

What is the process that the DOAS goes through to get the leaving air
temperature at set-point?



Typically, you need to create a “dummy space” and assign it to a “dummy
zone” then assign your first system to this zone.  If you already created
systems you can always open your .inp file and cut and paste the DOAS to the
top of the systems list so that it will become your first system.  Go ahead
and assign all of the outside air to your DOAS “dummy zone” and then
choose outside air from system for all of the systems that this DOAS serves.
It will only be able to find OA from systems above it on the component tree,
so make sure your DOAS is at the top.





Joe Fleming, E.I., LEED AP BD+C, BEMP



From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tiejun hu
Sent: Thursday, April 14, 2011 1:11 AM
To: equest-users
Subject: [Equest-users] FC+DOAS



hi equesters

            Dose anybody have experiences for FC+DOAS, in my modle, outdoor
air processed by independent air-condition unit, then supplied to room
directly, do not go through FC inlet. as far as i kown, outdoor air and
return air combined process in FC in some countries,like below picturebut On
the upper right corner,i see an outdoor air fan, is it an DOAS? if so ,how
to realize it in equest? and how to set in the tab "OA FROM SYSTEM"?

 any words will be appreciated!


yours sincere

 hi joe

       thanks for your reply,this is my Processing,, independent outdoor air
from DOAS are processed to S( isenthalpic with room N,H:90%), then mixed
with supply air from FC outnet(L), outdoor air doesn't undertake indoor
load.  Note that: my outdoor air do not get through FC, delivered to room
derectly.

    i doubt that , as your method, Whether outdoor air from DOAS will be
delivered to FC, flow through the fan in FC, then increase fan energy?

 thanks again!



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110414/77ca990c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 44733 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110414/77ca990c/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5634 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110414/77ca990c/attachment-0005.jpeg>


More information about the Equest-users mailing list