[Equest-users] app g economizer

Andy Phelps aphelps at barnesanddodge.com
Fri Apr 15 13:21:11 PDT 2011


I think for the purposes of App G, the answer is airside.  90.1 does
differentiate between air and water economizers:

 

economizer, air: a duct and damper arrangement and automatic

control system that together allow a cooling system to

supply outdoor air to reduce or eliminate the need for mechanical

cooling during mild or cold weather.

 

economizer, water: a system by which the supply air of a cooling

system is cooled indirectly with water that is itself cooled

by heat or mass transfer to the environment without the use of

mechanical cooling.

 

Haven't seen a CIR that addresses this, though.

 

 

Andy Phelps, PE, LEED AP | BARNES & DODGE, INC. |
aphelps at barnesanddodge.com | (o) 913-321-6444 | (c) 913-710-7915 | 

The information contained in this electronic message is confidential and
is or may be protected by trade secret protections, and/or other
applicable protections from disclosure.  If the reader of this message
is not the intended recipient, you are hereby notified that any use,
dissemination, distribution or reproduction of this communication is
strictly prohibited.  If you have received this communication in error,
please immediately notify us by calling 913-321-6444, or by e-mail to
front at barnesanddodge.com <mailto:front at barnesanddodge.com> , and
immediately delete this e-mail message and any attachments thereto.
Although this e-mail message and any attachments are believed to be free
of any virus or other defect that might negatively affect any computer
system into which it is received and opened, it is the responsibility of
the recipient to ensure that it is virus free and no responsibility is
accepted by Barnes & Dodge, Inc. for any loss or damage arising in any
way in the event that such a virus or defect exists. Thank you.

 

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Dahlstrom, Aaron
Sent: Friday, April 15, 2011 2:35 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] app g economizer

 

A simple Q -  

 

Does everyone agree that the App G baseline building is supposed to have
an air-side economizer (in the mentioned climates)?

 

There are some buildings where architectural choices make it difficult
to accommodate an air-side economizer.

 

Nonetheless, Section G3.1.2.6 appears to require modeling specifically
an air-side economizer for the baseline

 

I am thinking it could be a bit ambiguous depending on what you think
"outdoor air economizer" means. 

 

Has anyone seen interpretations clarifying this one way or the other?

Or submitted a CIR to allow water-side economizers in the baseline where
that is the industry standard for the building type?

 

THANKS,

 

Aaron Dahlstrom , PE, LEED(r) AP

In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414,
Philadelphia, PA 19102 

d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF:
215-735-7290

e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com
<http://www.in-posse.com/>  | akf web: www.akfgroup.com
<http://www.akfgroup.com/> 

 

 

 


This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended
recipient of this e-mail, do not duplicate or redistribute it by any
means. Please delete it and any attachments and notify the sender that
you have received it in error. Unintended recipients are prohibited from
taking action on the basis of information in this e-mail. E-mail
messages may contain computer viruses or other defects, may not be
accurately replicated on other systems, or may be intercepted, deleted
or interfered without the knowledge of the sender or the intended
recipient. If you are not comfortable with the risks associated with
e-mail messages, you may decide not to use e-mail to communicate with In
Posse. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110415/624f109a/attachment-0002.htm>


More information about the Equest-users mailing list