[Equest-users] parametric run

Bishop, Bill wbishop at pathfinder-ea.com
Tue Apr 19 07:37:55 PDT 2011


Vipin,

 

When I model cool roofs for ASHRAE Standard 90.1 Appendix G, I change
the absorptance of the roof construction to 0.55, per the
reflectance=0.45 allowance in Table G3.1.

 

 

 

Bill

 

William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP

Mechanical Engineer

 

 134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005

wbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>            
www.pathfinder-ea.com <http://www.pathfinder-ea.com/> 

P   Sustainability - the forest AND the trees. P    

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vipin
Sharma
Sent: Monday, April 18, 2011 7:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] parametric run

 

Hi....................
                          How parametric run is done in eQUEST. I am
beginner .Can anyone tell me
                         for cool roof parametric run.Thanks in advance.

Regards 
vipin sharma
student
Energy Engg. 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/45e461f7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/45e461f7/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 36845 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/45e461f7/attachment-0005.jpeg>


More information about the Equest-users mailing list