Nick Caton ncaton at smithboucher.com
Tue Aug 2 08:01:05 PDT 2011


Hi Ömer,

A1: If you're not conditioning the fresh air, then there's no reason to try and model this ventilation as a SYSTEM.  Assign a direct load to your meter.  Assign to a submeter if you wish to separately track its energies easily.  Further discussion in the archives if you need to ask how.

A2: A fractional schedule is necessary to model CO sensor-based controls.  If you're doing this under LEED:  90.1-2007 users manual, which offers specific schedules for specific occupancies (adapted from 90.1-1989, also used in the Washington State energy code IIRC)... has a table for parking garages.  Rather than provide an hourly fraction as with most other cases, it says Parking garage HVAC shall be "Based on likely use."  I interpret this as a prescriptive latitude to define and assign schedules appropriate to your system's behavior on a case-by-case basis.

A3: "Model the airflows" is a fairly vague query... Are these operating for user comfort?  If they're tied to a thermostat, it might be easiest to set them up as a system with a thermostat.  If they're just circulating/directing ventilation air alongside the main exhaust fan, then I'd treat them identically as a direct load to the meter, per A1.  I'd use an identical or modified schedule from that used for the exhaust fan, depending on whether they operate identically.

~Nick

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com 


-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ömer Moltay
Sent: Tuesday, August 02, 2011 6:05 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modelling Parking Garage Exhaust Combined with JetFans

Dear All,

In a building with 6 underground parking storeys, air is exhausted 
through a shaft and a single fan, while outside air is brought in 
through natural flows on another shaft. This is achieved by jet fans 
operating in each parking garage. The exhaust fan is variable speed 
controlled by CO sensors in the parking areas.

Q1: How can I assign 6 underground zones to a single exhaust fan? As far 
as I know, exhaust flows are assigned on a zone basis in eQuest?
Q2: How to model the speed variation of the exhaust fan? Any other way 
other than using schedules?
Q3: Can eQuest model the airflows caused by jet fans? Or should I just 
assign these as electric loads so that their electric consumption is 
taken into account?

Thank you,

Ömer Moltay, LEED AP BD+C, BREEAM Assessor
Mimta Ltd.
Hekimsuyu Cad. 559. Sk. No:39
34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
www.mimtarch.com
www.mimtasolar.com
www.eko-yapi.net
www.servogas.com

Sürdürülebilir Binalar Blog
http://surdurulebilirbina.blogspot.com

Green Building in Turkey on LinkedIn
http://www.linkedin.com/groups?gid=2278249


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list