[Equest-users] Baseline Heat Recovery
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Dec 1 06:37:45 PST 2011
Omer,
I would set ERV-LATENT-EFF to 0.50.
Additionally, if the baseline system is required to have an economizer
per G3.1.2.6, I would meet the G3.1.2.10 requirement "to bypass or
control the heat-recovery system to permit air economizer operation,
where applicable", by setting ERV-RUN-CTRL to WHEN-MIN-OA.
I guess it is a judgment call how to set all the other ERV variables.
Typically, I set them identical to the proposed ERV if there is one.
Regards,
Bill
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
omoltay at mimtarch.com
Sent: Wednesday, November 30, 2011 10:06 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Heat Recovery
Dear All,
How would you recommend modeling in eQuest the G3.1.2.10 requirement
with
its request that "50% energy recovery effectivness shall mean a change
in
the enthalpy of the outdoor air supply equal to 50% of the difference
between the outdoor air and return air at design conditions"?
Thanks,
Omer Moltay
Mimta
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/be1515b5/attachment.htm>
More information about the Equest-users
mailing list