[Equest-users] Economizer issue
Regis Bruant
RBruant at B2Qassociates.com
Thu Dec 29 12:35:36 PST 2011
Hi everyone,
I am trying to implement an economizer based on OA enthalpy on a baseline model that has an economizer set on OA temperature and have issue because I have an unexpected increased in gas usage on the proposed case.
The system I am working on consists of a VAV box containing a heating and cooling coil respectively attached to a Hot water loop and a chilled water loop (operating from March to October). It has terminal reheat coils at the zone level.
-The baseline economizer system is set on Outdoor air temperature high limit of 50F because of the low discharge air temperature of 52F.
-The proposed case economizer is set on an enthalpy high limit of 23BTU (and an OA temperature high limit of arbitrarily 100F because we want the economizer to be only limited by the enthalpy). The discharge air temperature was also reset because the system will be economizing with air temperature higher than the initial discharge temperature of 52F. It was reset from 52F to 63F as the Outdoor temperature varies from 52 to 73F.
Results:
-1st run: When running the discharge air setpoint reset based on OAT alone, we obtain substantial electrical and gas usage gain.
-2nd run: When running the discharge air setpoint reset based on OAT + the economizer based on OA enthalpy, we obtain even higher gain in electrical consumption but a lower gas usage gain.
Results numbers:
Baseline:
Elec: 14,582,599 kwh
Gas: 646,752 therms
1st run:
Elec: 14,439,619 kwh
Gas:587,782 therms
2nd run:
Elec: 14,319,200kwh
Gas: 607,876 therms
I do not understand why there is a gas usage increase on the 2nd run in comparison to the 1st run.
Has anyone been through the same issue? It would be very helpful to share any kind of info.
Thank you for your time,
Regis Bruant
Intern
B2Q Associates, Inc.
146 Main Street #2
North Andover, MA 01845
Office: 978.208.0609 x212
Fax: 978.719.6339
Mobile: 978.810.1858
Email: rbruant at B2Qassociates.com<mailto:rbruant at B2Qassociates.com>
www.b2qassociates.com<http://www.b2qassociates.com/>
The contents of this e-mail and any attachments are confidential and the property of the B2Q Associates, Inc. The e-mail contents are only to be used by the intended recipient of the e-mail. If you are not the intended recipient then use, disclosure, copying, distribution or reliance on the e-mail is prohibited. All professional advice from us should be obtained in writing (not e-mail).
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111229/33b92cb9/attachment.htm>
More information about the Equest-users
mailing list