[Equest-users] Concrete columns and beams
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Dec 1 07:00:50 PST 2011
Ali,
Welcome to energy modeling and to equest-users! We'll show you how deep
the rabbit hole goes.
You can either calculate an area-weighted U-factor for the wall/column
combination, or model the columns as separate surfaces. You can't just
specify that a wall contains columns. The area-weighted U-factor allows
a simpler building geometry but requires you to do the calculation, the
columns-as-separate-surfaces option requires you to use additional
vertices when defining the shell(s) in the wizard, and may add computing
time. You may want to model the columns separately to allow for the
shadows they cast and/or to show them visually in a 3-D view. The mass
of the columns may be thermally important as well depending in part on
your climate.
Regards,
Bill
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ali
Murat Tanyer
Sent: Thursday, December 01, 2011 8:40 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Concrete columns and beams
Dear all,
I am trying to model my first building. I have a very simple question:
I can select individual walls and edit their thermal properties.
However, there are concrete column and beam within the wall. These frame
elements are visible from inside and outside. Obviously, the U value of
my wall and the concrete frame elements are quite different. But I can
only define one U value for the wall.
Is there a way to specify that my wall contains concrete beams/columns
with specified U values.
Thanks in advance.
Ali
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list