[Equest-users] Underheating warning for bunch of zones
Nikola Kravik
NKravik at willdan.com
Thu Dec 1 15:15:14 PST 2011
Thanks Neil, yes your input coincide with rest of the feedback I received personally through the equest users group; indeed it was the Heating tab and the Heat/reheat set's that I've assumed if I leave black will be fine but they weren't.
I appreciate your feedback.
Best,
Nikola
Nikola Kravik, LEED AP [cid:image001.gif at 01CCB03C.06B31DF0]
Project Engineer
Willdan Energy Solutions
11875 Dublin Boulevard, Suite A-201
Dublin, California 94568
T. 925.556.2600 ext. 1228
C. 925.719.5883
F. 925.556.1444
nkravik at willdan.com<mailto:nkravik at willdan.com>
www.willdan.com/energy<http://www.willdan.com/energy>
[cid:image002.jpg at 01CCB03C.06B31DF0]
From: Neil Bulger [mailto:nbulger at integralgroup.com]
Sent: Thursday, December 01, 2011 3:12 PM
To: Nikola Kravik; Rob Hudson
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Underheating warning for bunch of zones
Nikola,
I opened the model and you need to specify in the Air-side systems that are attached to the HW loop a design deck heating setpoint and a reheat delta-T setpoint. eQuest will not auto-input these items for you so, when it goes to size a system, it has nothing to base the calculations on.
[cid:image003.jpg at 01CCB03C.06B31DF0]
The model runs now so, see if you can move forward from there and post more questions if you have em.
Cheers,
Neil Bulger
Project Engineer
________________________________
I N T E G R A L
GROUP
427 13th Street, Oakland CA 94612
510 663 2070 x 235
nbulger at integralgroup.com<mailto:nbulger at integralgroup.com>
www.integralgroup.com<http://www.integralgroup.com/>
DEEP GREEN Engineering.
________________________________
[cid:image004.png at 01CCB03C.06B31DF0]<http://www.linkedin.com/groups?about=&gid=3830399>[cid:image005.png at 01CCB03C.06B31DF0]<http://www.facebook.com/#!/pages/Integral-Group-Inc/213422145352140> [cid:image006.png at 01CCB03C.06B31DF0] <http://twitter.com/#!/IntegralGroupCA> [cid:image007.png at 01CCB03C.06B31DF0] <http://www.youtube.com/user/IntegralGroupOakland> [cid:image008.png at 01CCB03C.06B31DF0] <http://www.integralgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nikola Kravik
Sent: Wednesday, November 30, 2011 3:00 PM
To: Rob Hudson
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Underheating warning for bunch of zones
Rob/all,
I don't have baseboards, it's basic VAV/w reheat system-I was trying to use the baseboards just to see if the zone heating kicks in.
I've attached the zip file, it's giving me the same warning that the zones are under heated and also 1 error that the "hot water loop has zero design flow".
I'm stuck and not sure how to go about it. Please point/help me understand how to go about the error fix....
I appreciate your feedback.
Best,
Nikola
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Tuesday, November 29, 2011 12:03 PM
To: Nikola Kravik
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Underheating warning for bunch of zones
I would first check your system level inputs. Have you used a VAV system? if so, you need to know that these systems don't like to use the heating coil in the air handler and therefore you need to specify a reheat coil size and a preheat coil. Also, if you have baseboards in the model, they don't like to operate very well when set to activate to outdoor conditions. I always set the baseboard control to thermostat.
Hopefully these few tips help out.
Rob
On Tue, Nov 29, 2011 at 2:52 PM, Nikola Kravik <NKravik at willdan.com<mailto:NKravik at willdan.com>> wrote:
hi,
I'm simulating CHW Plant with CAV AHU's and bunch of packaged/split system units around supporting areas of the hospital/clinic.
I get the warning messages similar to below for almost all my zones and my gas heating hot water is extremely low, no matter what I try do on the heating side. I added baseboards but it didn't make a difference-still have bunch of zones underheated looking at the ss-o's.
Do you any other hints you can share where else to look for the HHW low consumption?
Best,
Nikola
[cid:image009.png at 01CCB03C.06B31DF0]
[cid:image010.jpg at 01CCB03C.06B31DF0]
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 1348 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3030 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 28315 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1704 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1784 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1781 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1978 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 2562 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 47313 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 92188 bytes
Desc: image010.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111201/75afb64e/attachment-0008.jpg>
More information about the Equest-users
mailing list