[Equest-users] Baseline Fan power pressure drop adjustmentclarification
Otto Schwieterman
oschwieterman at fhai.com
Mon Dec 5 13:46:06 PST 2011
Eduardo,
I have not received this comment but would accept what the reviewer
says. Even if it is not in ASHRAE 90.1 2004 Appendix G, the reviewer has
final authority on items not directly stated in ASHRAE Appendix G.
You can try to argue it but I don't see the reviewer accepting it since
there is not a clear answer to how it should be modeled. Usually you
need documentation if you are going to try to change the reviewer's
mind. Since the baseline model does not include energy recovery it does
not make sense to take the pressure drop for energy recovery into the
fan consumption for the baseline model.
Good luck,
Otto
From: Eduardo Galeano [mailto:egaleano at EMEGroup.com]
Sent: Monday, December 05, 2011 3:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Fan power pressure drop
adjustmentclarification
Hello Everyone,
Recently we received a LEED review comment related to EAc1 for one of
our projects and we would like to get some of your opinions on this
issue in case anyone else experienced this problem before. The project
is a laboratory building and we are filing under LEED NC v2.2 using
ASHRAE 90.1-2004. We implemented addendum ac to ASHRAE 90.1-2004 to
claim the baseline fan power pressure adjustments found in section 6 of
90.1. The comment is as follows:
"It appears that a pressure credit is being taken for exhaust air heat
recovery for fan power in the Baseline Case. However, while exhaust air
heat recovery is present in the Proposed Case, it is not present in the
Baseline Case and therefore the pressure credit for fan power cannot be
taken. If appealing this credit, remove all Baseline Case fan power
pressure credits for exhaust air heat recovery, and update the model and
template results."
Based on our modeling methodology, heat recovery is not required in the
baseline and this seems to have been accepted. However, what we don't
understand is why the baseline fan pressure adjustment cannot be used
for heat recovery elements present in the proposed design if the
baseline does not require it. Our understanding was that baseline fan
power pressure drop adjustments were mutually exclusive of any
requirement of baseline system components (e.g. heat recovery).
We are also aware that in ASHRAE 90.1-2007 Appendix G, underneath table
G3.1.2.9 the following text is included:
"Do not include pressure drop adjustments for evaporative coolers or
heat recovery devices that are not required in the baseline system by
Section G3.1.2.10."
However, such sentence is not included in any addenda to ASHRAE
90.1-2004 as far as we can tell, and it should only be considered for
projects filing under ASHRAE 90.1-2007. Any thoughts? Is it not
acceptable to claim the baseline fan pressure credits for system
components not required in the baseline model?
Thanks in advance.
Eduardo
Eduardo Galeano, LEED AP
EME Consulting Engineering Group, LLC
159 West 25th Street, 5th Floor
New York, NY 10001
Tel: 212-529-5969
Fax: 212-529-6023
www.emegroup.com
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity. If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111205/0acc8a89/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1822 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111205/0acc8a89/attachment-0002.jpeg>
More information about the Equest-users
mailing list