[Equest-users] Radiant Heating and Cooling?
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Tue Feb 8 08:26:01 PST 2011
Hi Julie,
1. You can "represent" radiant ht & clg in eQuest, by modifying a system
to *act* like a radiant system, however be mindful that because DOE2
can't do this explicitly there will be some discrepancies from real life,
but it still can be a fairly realistic representation and measurment of the
system performance. To do this you will want to choose a Fan Coil system
for your HVAC type and turn down your fan power in the FC units to zero.
You will also want to probably use a DOAS & Dummy Zone approach for your
ventilation systems. This is an approach to use in eQuest. I can send you
an example file of a Dummy zone for you to look through and learn from. You
will also want to read about the FC system in another DOE2 document I will
also send you (off list). Once you understand how DOE2 represent a Fan Coil
system, then you will understand how you can change it to better act like a
radiant system. Others might consider using the PIU system in eQuest, but
I have found by my experience that PIU's are better for representing Active
Chilled Beam systems, and Fan Coils are better to represent radiant only
systems. I'm happy to share more of my sim experience with radiant systems,
but I'm also curious to hear other's simulators experiences
with representing radiant systems in eQuest too.
2. When you say "louvers" I'm assuming you are referencing external
shading devices. Yes you can input vertical exterior shades on the outside
of your building by using the Building Shade inputs. This can only be done
in DDedit mode, and the inputs are based on your XYZ coordinates of the
building space. I will send you a 3rd document (Modeling Procedures Quck Ref
Guide) and you can learn how to input these shades in Chapter 8 of the
document.
Feel free to write back to the list or to me if you have more questions.
You will find lots of great simulators who are always more than willing to
share thier experiences with new users.
Hope this helps,
Pasha
Korber Energy Consultants
www.korberenergy.com
2011/2/8 Ju-Yeon Julie Shin <juyeon519 at hotmail.com>
> Hello everyone, this is Julie Shin.
>
> 1. I am curious whether it is possible to add "radiant heating and cooling"
> for eQUEST simulations or not.
> If it is possible, could anyone please let me know how to do so?
>
> 2. Is it also possible to add vertical louvers? I have tried adding
> horizontal louvers, but not the vertical ones.
>
> Thank you everyone and have a nice day.
>
> Julie Shin.
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/d6637387/attachment-0001.htm>
More information about the Equest-users
mailing list