[Equest-users] Fenestration and Window to Wall Ratio
James Newman
James.Newman at me-engineers.com
Tue Feb 8 16:29:19 PST 2011
Correct, so if your proving prescriptive compliance you can use below grade walls, while if your proving compliance through performance modeling then you can only usie above grade walls per ASHRAE 90.1 Appendix G.
The question that I still have is should the whole building be averaged for fenestration percentage or should each face have its own percentage?
James M. Newman, EIT, LEED AP
project engineer / energy analyst
From: Dana Troy [mailto:DTroy at glumac.com]
Sent: Tuesday, February 08, 2011 5:09 PM
To: James Newman
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Fenestration and Window to Wall Ratio
90.1 Appendix G states: "Vertical fenestration areas for new buildings and additions shall equal that in the proposed design or 40% of gross above-grade wall area, whichever is smaller."
If you are using 90.1 as your State's code, then you can include the below-grade wall area. If you are modeling using Appendix G, then you cannot include the below grade wall area in your calculations.
-Dana
Dana Troy
Senior Energy Analyst
GLUMAC | 503.227.5280
-----Original Message-----
From: James Newman [mailto:James.Newman at me-engineers.com]
Sent: Tuesday, February 08, 2011 3:29 PM
To: Sunayana Jain
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fenestration and Window to Wall Ratio
This paragraph comes directly out of the ASHRAE 90.1-2007 User Manual:
"Window-Wall Ratio: The window-wall ratio is the ratio of vertical fenestration area to gross exterior wall area. The fenestration area is the rough opening, i.e., it includes the frame, sash, and other nonglazed window components. The gross exterior wall is measured horizontally from the exterior surface; it is measured vertically from the top of the floor to the bottom of the roof. The gross exterior wall area includes below-grade as well as above-grade walls. It is necessary to calculate the window-wall ratio with all compliance options, since this information is need with the prescriptive option, the trade-off option, and the energy cost budget method."
James M. Newman, EIT, LEED AP
project engineer / energy analyst
-----Original Message-----
From: Sunayana Jain [mailto:sunayana_jain at neo.tamu.edu]
Sent: Tuesday, February 08, 2011 4:20 PM
To: James Newman
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fenestration and Window to Wall Ratio
Hi James,
As per my understanding, window wall ratio is considered for above grade walls only for each orientation of building (not floor to floor).
Thanks,
Sunayana Jain
LEED AP, EIT
Energy Engineering Specialist
----- Original Message -----
From: "James Newman" <James.Newman at me-engineers.com>
To: equest-users at lists.onebuilding.org
Sent: Tuesday, February 8, 2011 5:29:50 PM GMT -05:00 US/Canada Eastern
Subject: [Equest-users] Fenestration and Window to Wall Ratio
When calculating the window to wall ratio for your baseline building, should you calculate this percentage as
· an entire building?
· each building elevation?
· every floor elevation?
Has anyone had an interpretation on this issue? I was reading through the 90.1 User manual and discovered that both above grade walls and below grade walls should be considered for the wall to wall ratio which leads me to believe the calculation should be done as a whole building percentage. Just curious if someone knows the correct answer.
Thanks,
James M. Newman, EIT, LEED AP
project engineer / energy analyst
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110208/abfb36d0/attachment-0001.htm>
More information about the Equest-users
mailing list