[Equest-users] Fenestration and Window to Wall Ratio

Nick Caton ncaton at smithboucher.com
Wed Feb 9 07:35:36 PST 2011


I’d agree – I’ve always taken the 40% WWR mark in context to mean the gross above-grade building surfaces (minus the roof/skylights of course).  Pretty simple.

 

If 90.1 intended to assign a prescriptive maximum WWR per face, it would say so.  Further, rather than a single value I would expect to see a chart showing different maximum ratios for each orientation, and also broken out either by “solar zone” (using a solar map), or perhaps more simply by latitude. 

 

~Nick


PS:  I realize Joe’s example is just that, an example, but if you’re ever modeling a 100% glass orientation, it’s worth nothing that any spandrel glass constructions that don’t transmit light aren’t “vertical fenestrations” as defined in the definitions, and so wouldn’t count towards the WWR ratio check/calcs.

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fleming, Joe
Sent: Tuesday, February 08, 2011 6:41 PM
To: James Newman; Dana Troy
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fenestration and Window to Wall Ratio

 

The whole building is the way I have always read it.  

So you can have an all glass North wall (100%) and then 10% glass for E,W,&S and have a total window-wall ratio of 32.5%.   But if you have a North wall with 100% glass and an E,W,&S wall with 40% glass, you now have to prorate each exposure down.  

--> (1+0.4+0.4+0.4) / 4 = 55%  which is greater than 40%.  So, multiply each exposure by 0.4/0.55, and your new window-wall ratios would be N=72.7%, E,W,&S = 29.1%.

 

 

Joe Fleming

E.I., LEED AP BD+C, BEMP

Mechanical Engineer II

 

TLC Engineering for Architecture
Your 2030 Challenge Partner

 

800 Fairway Drive, Suite 250

Deerfield Beach, FL 33441-1816

 

phone: 

954-418-9096

fax: 

954-418-9296

direct: 

954-418-4591

website: 

www.tlc-engineers.com <http://www.tlc-engineers.com/> 

 

  <http://www.tlc-engineers.com/> 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James Newman
Sent: Tuesday, February 08, 2011 7:29 PM
To: Dana Troy
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fenestration and Window to Wall Ratio

 

Correct, so if your proving prescriptive compliance you can use below grade walls, while if your proving compliance through performance modeling then you can only usie above grade walls per ASHRAE 90.1 Appendix G.

 

The question that I still have is should the whole building be averaged for fenestration percentage or should each face have its own percentage?

 

James M. Newman, EIT, LEED AP

project engineer / energy analyst

 

From: Dana Troy [mailto:DTroy at glumac.com] 
Sent: Tuesday, February 08, 2011 5:09 PM
To: James Newman
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Fenestration and Window to Wall Ratio

 

90.1 Appendix G states: "Vertical fenestration areas for new buildings and additions shall equal that in the proposed design or 40% of gross above-grade wall area, whichever is smaller."

 

If you are using 90.1 as your State's code, then you can include the below-grade wall area. If you are modeling using Appendix G, then you cannot include the below grade wall area in your calculations.

 

-Dana

 

 

Dana Troy

Senior Energy Analyst

GLUMAC | 503.227.5280

 

 

 

 

-----Original Message-----
From: James Newman [mailto:James.Newman at me-engineers.com] 
Sent: Tuesday, February 08, 2011 3:29 PM
To: Sunayana Jain
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fenestration and Window to Wall Ratio

 

This paragraph comes directly out of the ASHRAE 90.1-2007 User Manual:

 

"Window-Wall Ratio: The window-wall ratio is the ratio of vertical fenestration area to gross exterior wall area. The fenestration area is the rough opening, i.e., it includes the frame, sash, and other nonglazed window components.  The gross exterior wall is measured horizontally from the exterior surface; it is measured vertically from the top of the floor to the bottom of the roof. The gross exterior wall area includes below-grade as well as above-grade walls. It is necessary to calculate the window-wall ratio with all compliance options, since this information is need with the prescriptive option, the trade-off option, and the energy cost budget method."

 

James M. Newman, EIT, LEED AP

project engineer / energy analyst

 

 

-----Original Message-----

From: Sunayana Jain [mailto:sunayana_jain at neo.tamu.edu] 

Sent: Tuesday, February 08, 2011 4:20 PM

To: James Newman

Cc: equest-users at lists.onebuilding.org

Subject: Re: [Equest-users] Fenestration and Window to Wall Ratio

 

Hi James,

 

As per my understanding, window wall ratio is considered for above grade walls only for each orientation of building (not floor to floor).

 

Thanks,

 

Sunayana Jain

 

LEED AP, EIT

 

Energy Engineering Specialist

 

----- Original Message -----

From: "James Newman" <James.Newman at me-engineers.com>

To: equest-users at lists.onebuilding.org

Sent: Tuesday, February 8, 2011 5:29:50 PM GMT -05:00 US/Canada Eastern

Subject: [Equest-users] Fenestration and Window to Wall Ratio

 

 

 

 

 

When calculating the window to wall ratio for your baseline building, should you calculate this percentage as 

 

  

 

·          an entire building? 

 

·          each building elevation? 

 

·          every floor elevation? 

 

  

 

Has anyone had an interpretation on this issue?  I was reading through the 90.1 User manual and discovered that both above grade walls and below grade walls should be considered for the wall to wall ratio which leads me to believe the calculation should be done as a whole building percentage. Just curious if someone knows the correct answer. 

 

  

 

Thanks, 

 

  

 

James M. Newman, EIT, LEED AP 

 

project engineer / energy analyst 

 

  

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110209/f189484a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110209/f189484a/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5272 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110209/f189484a/attachment-0002.gif>


More information about the Equest-users mailing list