[Equest-users] Heating mode stuck at minimum flow rate
Brian Fountain
bfountain at greensim.com
Sun Jan 16 21:31:06 PST 2011
You need to change your zone thermostat action from Proportional to
Reverse Action.
On 1/16/2011 9:24 PM, Roselin Osser wrote:
>
> Hi folks,
>
> I'm modeling a packaged VAV system (PVAVS) serving only one zone. The
> maximum airflow the unit can provide is 450,000 cfm, which I have
> entered in as an airflow parameter. The problem is that whenever the
> system goes into heating mode, the total cfm goes to minimum airflow
> (observed from hourly output), even when more heating is needed, so I
> end up with a lot of underheated hours. The minimum airflow is
> calculated from the 10% outdoor air ratio I have entered. I have
> tried adjusting the HMAX-FLOW-RATIO field to allow the heating airflow
> to go above the minimum if necessary, but the field seems to have no
> effect. I have a reverse action thermostat in the zone. Anyone else
> run into this? There must be some other parameter I'm using that is
> preventing the field from working. Any advice would be appreciated,
> as I have tried a lot of input variations and none of them allowed the
> heating minimum flow to increase when more heat is needed. I'm using
> eQuest 3.64.
>
> Thanks for your help!
>
> Rosie
>
> Roselin Osser, BEMP, LEED AP
>
> Building Science Corporation
>
> 30 Forest Street
>
> Somerville, MA 02143
>
> 978-589-5100 x 5284
>
> fax: 978-589-5103
>
> Building Science Corporation
> Somerville MA | Waterloo ON
> www.buildingscience.com <http://www.buildingscience.com/>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1191 / Virus Database: 1435/3384 - Release Date: 01/16/11
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110117/5d3ea4a4/attachment-0002.htm>
More information about the Equest-users
mailing list