[Equest-users] Air-Cooled EIR Curves
Nick Caton
ncaton at smithboucher.com
Wed Jan 19 15:43:56 PST 2011
Hi John,
Hmm… intuitively I think this makes sense, but I haven’t actually gone through creating a set of custom packaged DX curves before - lets’ first verify we’re looking at the same definition:
Volume 2: Dictionary > HVAC Components > SYSTEM > Cooling Equipment > DX Cooling
COOL-EIR-FT
Takes the U-name of a bi-linear or bi-quadratic curve that describes the Electric Input Ratio for cooling as a function of entering wet-bulb temperature and outdoor dry-bulb temperature (for direct expansion coils) or entering wet-bulb temperature and entering water temperature for a Water Loop Heat Pump (HP) system. At ARI conditions, the value of the curve should be 1.
I’m pretty sure the entering wet-bulb is that found entering the evaporator coil - the mixed air about to be conditioned. If you check out a typical set of packaged DX unit performance tables (If you want a specific example to follow along, I’ve just cracked open an engineering guide for the Lennox LGH series <http://tech.lennoxintl.com/C03e7o14l/HS7CbNGGFw/ehb_lgh_abox_1010.pdf> * to page 21), you’ll find they’ve got OA DB along one axis (85/95/105/115) and Entering WB along the other axis (63/67/71). It would appear the same tables could also be used to reference data for COOL-CAP-FT and COOL-SH-CAP curves.
Make sense now?
‾Nick
*Disclaimer: I have no particular ties or intent/business to advocate Lennox over their competitors - all of their major competitors publish similar reference/sizing tables, and this particular unit’s guide just happened to be near the top of my reference stack.
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John T. Forester
Sent: Wednesday, January 19, 2011 4:50 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Air-Cooled EIR Curves
Quick question,
When creating custom EIR fT and EIR fPLR curves for air-cooled packaged DX units with digital scroll compressors, what are the two independent variables? The DOE2 help says to use entering wet-bulb and outside air dry-bulb. Where is the entering wet-bulb temperature measured? Intuitively, this doesn’t seem correct to me.
Thanks,
John
John T. Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated Services I 617.658.9008 tel I 617.244.3753 fax I One Gateway Center Suite 506, Newton MA 02458 I www.bvhis.com I Hartford ● New Haven ● Boston
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110119/25dc8b89/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110119/25dc8b89/attachment-0002.jpeg>
More information about the Equest-users
mailing list