Omar:
You've got me double-checking my ASHRAE 90.1-07!
There is no call in Table G3.1.1B for system 5 to have fan powered terminal units.
Also, section G3.1.3.4 only provides instructions for fan powered terminal units for systems 6 and 8.
So I would say you should omit fan powered boxes from System 5.
Where we have fan powered boxes - either in the design, or in baseline system 6/8, we typically model with a PIU system. It sounds like you want a packaged system - the default is for PIU to have chilled water, but you can change the cooling-source to DX and spec an air- or water-cooled condenser, once you've created the system.
The power (and type) of the terminal unit fans is actually specified at the zone level. I've attached the section of the DOE-2 dictionary that explains how this works. See sections "terminal-type" and "zone fans".
Aaron
Aaron Dahlstrom , PE, LEED® AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com | akf web: www.akfgroup.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ömer Moltay
Sent: Friday, January 21, 2011 11:03 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] PVAVS System Terminal Box Fans
Hello,
Does eQuest model PVAVS systems with fan powered terminal boxes? If so,
how do you specify the power of these fans?
Additionally, in case of Appendix G modelling for LEED, is one supposed
to model System 5 with fan powered boxes or not?
Thank you,
Omer Moltay, LEED AP
Mimta
-----
Bu iletide virüs bulunmadı.
AVG tarafından kontrol edildi - www.avg.com
Sürüm: 10.0.1191 / Virüs Veritabanı: 1435/3393 - Sürüm Tarihi: 20.01.2011
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: DOE22Vol2-Dictionary_47f-2.pdf
Type: application/pdf
Size: 4663804 bytes
Desc: DOE22Vol2-Dictionary_47f-2.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110121/0c828aa8/attachment-0002.pdf>
More information about the Equest-users
mailing list