Yes Omar,
the reset control method is crucial to total energy comsuption. it delays reheat start time and can be combined wth chiller water reset control.
I think you should get to know detail control logic of proposed VAV system from control schmetic drawings of AHU.Maybe you can ask the designer of HVAC system or related control system. Not every VAV system with supply temperature reset.

Regards
Jenny
________________________________________
From: Omar Katanani [omar at ecoconsulting.net]
Sent: 24 January 2011 20:31
To: Jenny Zhang; Ömer Moltay; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] G3.1.3.12 Supply Air Temperature Reset

Dear Jenny,

Do you have an idea of what shall we put for the Proposed Case?

I have a regular VAV system serving multiple zones. I tried 2 simulations: 1 with the Cool Control being "Constant" and 1 with the Cool Control being "Warmest" (similar to the baseline). I got an improvement of 17.5% in the first case, and 20.2% in the second case. I thought this parameter was not that significant, but it turned out to be so!

Which option do you suggest to adopt for the Proposed Scenario?

Many thanks!
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net

EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel:          +961 (0) 1 971 266
Mobile:    +961 (0) 3 045 045

EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel:  +44 (0) 207 939 0989
Fax:  +44 (0) 207 939 0981
Website: www.ecoconsulting.net


-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jenny Zhang
Sent: 21 January 2011 04:35
To: 'Ömer Moltay'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] G3.1.3.12 Supply Air Temperature Reset

Hi Omer,
you can find reset option in the airside system screen(COOLING).
my approach is to choose reset>warmest>airflow first.(For VAV system I think the airflow will reduce first to satisfy load then the supply air temperature could rise at the minimum air flow rate.)
the dealt t for reset is according to ASHRAE 90.1.

Regards
Jenny Z



-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of ?mer Moltay
Sent: 2011年1月20日 23:54
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] G3.1.3.12 Supply Air Temperature Reset

Dear All,

In eQuest, how can the air temperature for cooling in a VAV system be
reset as required by G3.1.3.12?

Thank you,

Omer Moltay, LEED AP
Mimta Ltd.


-----
Bu iletide virüs bulunmadı.
AVG tarafından kontrol edildi - www.avg.com
Sürüm: 10.0.1191 / Virüs Veritabanı: 1435/3391 - Sürüm Tarihi: 19.01.2011

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


More information about the Equest-users mailing list