Omar,
U-factors describe heat transfer over an area (ft2). F-factors are very
similar except they describe heat transfer over a lineal foot (that may
be where the 'F' comes from... not sure) of perimeter.
There is not a straight conversion between U and F factors. F-factors
are accounting for heat transfer through multiple planes (the
wall/footing and the floor), and insulation present along one and/or the
other has slightly different effects.
While you could dig up the science/math behind it all, I find
representative F-factors are most easily found and used from 90.1
Appendix A - specifically read section A6 and the referenced table A6.3.
I believe ASHRAE Fundamentals may have a similar table if you want to
dig up other possibilities - I think theirs varies based on degree
days... but it's been awhile...
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Monday, January 24, 2011 6:38 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] F-Factor of ASHRAE 90.1
James,
I did not understand the appendix exactly! Isn't there 1 value for
converting between F-value and U-value that anyone can help me with?
Thanks!
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
________________________________
From: James Newman [mailto:James.Newman at me-engineers.com]
Sent: 19 January 2011 18:38
To: Omar Katanani; equest-users at lists.onebuilding.org
Subject: RE: F-Factor of ASHRAE 90.1
Omar,
Look in Appendix A in ASHRAE 90.1 to figure out what construction you
need to meet the appropriate F-Value.
James M. Newman, EIT, LEED AP
project engineer / energy analyst
M-E Engineers, Inc. <http://www.me-engineers.com/>
10055 west 43rd avenue
wheat ridge, co 80033
office: 303.421.6655
direct: 720.898.3148
james.newman at me-engineers.com <mailto:james.newman at me-engineers.com>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Wednesday, January 19, 2011 9:08 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] F-Factor of ASHRAE 90.1
Dear all,
I read numerous forum discussions and articles about the F-factor. My
question is much simpler!
For LEED purposes, ASHRAE 90.1 requires the F-factor for the unheated
slab-on grade floor in climate zone 3 to be F-1.264
I do not have insulation in my project.
I go to my floor construction makeup in eQUEST, and I have to enter the
U-value.
The question is: How can I transform the F-1.264 to a U-value that I can
enter into eQUEST?
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110124/17b9abe3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110124/17b9abe3/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110124/17b9abe3/attachment-0005.jpeg>
More information about the Equest-users
mailing list