Jackson, Alan ajackson at klingstubbins.com
Thu Jul 7 13:03:15 PDT 2011


Have you tried reverse laying the interior wall? If the interior wall was defined in the sunspace, then the material layer is reversed where the interior material is layer on the sunspace side and exterior is on the interior zone side.


O  |<-GLASS [  S  ] INT-SURFACE->||<-EXT-SURFACE  [  I  ]
U  |        [  U  ]              ||               [  N  ]
T  |        [  N  ]              ||               [  T  ]
D  |        [  S  ]              ||               [  .  ]
O  |        [  P  ]              ||               [  Z  ]
O  |        [  A  ]              ||               [  O  ]
R  |        [  C  ]              ||               [  N  ]
   |<-GLASS [  E  ] INT-SURFACE->||<-EXT-SURFACE  [  E  ]

So let's say your interior wall was brick faced. The brick surface would actually be the interior layer where normally it would be the exterior layer on a standard wall exposure. Put simpler “inside” is the side in the space in which the wall was defined.

See if that helps.


Alan Jackson, LEED AP
KlingStubbins

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ercoli, Christopher
Sent: Thursday, July 07, 2011 2:16 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQUEST Sunspace

Has anyone in the group used the sunspace option in eQUEST?  I have tried it and  it blew up in LOADS   Following is the .inp description of the Sunspace:

"EL1 North Perim Spc (G.N1)" = SPACE           
   X                = -25.25
   Y                = 109.6
   AZIMUTH          = 51.024
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "EL1 Bldg OffEq Sch", 
         "EL1 Bldg OffEq Sch" )
   INF-SCHEDULE     = "ZG1-S1 (UVT) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.0563044
   PEOPLE-HG-LAT    = 217.268
   PEOPLE-HG-SENS   = 250
   LIGHTING-W/AREA  = ( 1.14175 )
   EQUIPMENT-W/AREA = ( 0, 0, 0.791 )
   SUNSPACE         = YES
   AREA/PERSON      = 165.463
   POLYGON          = "EL1 Space Polygon 1"
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (79%)*
   ..
"EL1 North Wall (G.N1.E1)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V4
   SHADING-SURFACE  = YES
   ..
"EL1 North Win (G.N1.E1.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 0.108333
   X                = 0.808333
   Y                = 0.938333
   HEIGHT           = 7.17333
   WIDTH            = 138.803
   FRAME-CONDUCT    = 1.306
   SPACER-TYPE      = INSULATED
   ..
"EL1 SW Wall (G.N1.I1)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 WNW Perim Spc (G.WNW4)"
   CONSTRUCTION     = "Sunspace Wall construction"
   LOCATION         = SPACE-V1
   ..
"EL1 South Wall (G.N1.I2)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C5)"
   CONSTRUCTION     = "Sunspace Wall construction"
   INT-WALL-TYPE    = STANDARD
   LOCATION         = SPACE-V2
   ..
"Sunspace Window" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   X                = 1
   Y                = 6.5
   HEIGHT           = 2
   WIDTH            = 122
   C-WELL-HEIGHT    = 6.5
   C-WELL-WIDTH     = 1
   ..
"EL1 SSE Wall (G.N1.I3)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 SE Perim Spc (G.SE2)"
   CONSTRUCTION     = "Sunspace Wall construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (G.N1.I4)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Plnm (G.N6)"
   CONSTRUCTION     = "Air Ceiling of Sunspace"
   INT-WALL-TYPE    = AIR
   LOCATION         = TOP
   ..
"EL1 Flr (G.N1.U1)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UFCons (G.N1.U2)"
   LOCATION         = BOTTOM
   ..

Following is the system description of the sunspace:

"EL1 North Perim Zn (G.N1)" = ZONE            
   TYPE             = CONDITIONED
   MIN-FLOW-RATIO   = 1
   BASEBOARD-RATING = -25605.4
   FLOW/AREA        = 0.25
   OA-FLOW/PER      = 18.2732
   SS-FLOW-T-SCH    = "Max T for SS heating Annual"
   SS-VENT-CST      = 5
   SS-VENT-WND      = 0.2
   SS-VENT-TEMP     = 0.2
   SS-VENT-T-SCH    = "Vent T Annual Schedule"
   SS-VENT-SCH      = "Sunspace Venting Schedule"
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (UVT) Heat Sch"
   DESIGN-COOL-T    = 75
   BASEBOARD-CTRL   = THERMOSTATIC
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 North Perim Spc (G.N1)"
   ..
"EL1 North Perim Pl Zn (G.N6)" = ZONE            
   TYPE             = UNCONDITIONED
   DESIGN-HEAT-T    = 67
   DESIGN-COOL-T    = 75
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 North Perim Plnm (G.N6)"

Following is the error message

***ERROR***********************************************************************
In routine TEMDEV for ZONE EL1 North Perim Pl Zn (G.N6)     on  2/10 hr 11 (InitialFlg =  0)
  SUNSPACE INTERIOR-WALL calculations produced bad values:
  CSSVEC (convection) =           0. CSSVEC (conduction) =     7294864.
  This would cause a  262. degree ZONE temperature change.   Values are being ignored.
  Check wall definitions for errors and report this inp/lib/wth to DOE-2 support.

***ERROR***********************************************************************
In routine TEMDEV for ZONE EL1 North Perim Zn (T.N11)       on  2/10 hr 11 (InitialFlg =  0)
  SUNSPACE INTERIOR-WALL calculations produced bad values:
  CSSVEC (convection) =           0. CSSVEC (conduction) =   176604512.
  This would cause a 6794. degree ZONE temperature change.   Values are being ignored.
  Check wall definitions for errors and report this inp/lib/wth to DOE-2 support.

Any ideas as to where I went wrong?

- Christopher Ercoli 
 
 