Abhinav Devra,

Weather data for Bangkok is available at the following website:

http://apps1.eere.energy.gov/buildings/energyplus/cfm/weather_data3.cfm/region=2_asia_wmo_region_2/country=THA/cname=Thailand

The data is in the format required for EnergyPlus, not eQUEST. If you want
to convert this to a .BIN file compatible with eQUEST, download the
"EQ_WthProc" program at the following:

http://doe2.com/index_wth.html

This can be a bit tricky, so be sure to follow the instructions carefully.

Good luck,

Andrew

On Fri, Jul 8, 2011 at 5:36 AM, <Abhinav.Devra-EXT at jci.com> wrote:

>
> Hello All
>
> If anybody has used a weather file for Pattaya Island (Thailand), kindly
> share the weather file / link.
>
> Else do let me know about the nearest possible weather location, from where
> the useful "bin" file can be taken.
>
> Thanks & Regards
>
> Abhinav Devra
>