[Equest-users] URGENT: Window U-values: Total window assembly v/s Glass only
Carol Gardner
cmg750 at gmail.com
Fri Jul 29 11:35:17 PDT 2011
This came off of the Window website:
WINDOW 6.3 is a publicly available computer program for calculating total
window thermal performance indices (i.e. U-values, solar heat gain
coefficients, shading coefficients, and visible transmittances). WINDOW 6.3
provides a versatile heat transfer analysis method consistent with the
updated rating procedure developed by the National Fenestration Rating
Council (NFRC) that is consistent with the ISO 15099 standard. The program
can be used to design and develop new products, to assist educators in
teaching heat transfer through windows, and to help public officials in
developing building energy codes.
* *
On Fri, Jul 29, 2011 at 11:26 AM, Robby Oylear <robbyoylear at gmail.com>wrote:
> Carol,
>
> I have to take exception to this:
> "As far as NFRC, your Solarban glass data is NFRC rated which should be
> good enough, I think. It's rare in commercial buildings to have a rating for
> the entire window."
>
> From my first response:
> In order to meet LEED EAp2 Minimum Energy Performance, the project must
> comply with all mandatory provisions of ASHRAE 90.1-2007. Section 5.4.2
> Fenestration and Doors requires that fenestration performance be determined
> per section 5.8.2. Section 5.8.2.4 U-factor requires that the U-factor for
> the overall fenestration area (including framing) be determined in
> accordance with NFRC 100. If you do not have NFRC data available, values
> from section A8.2 are the only acceptable alternative.
>
> NFRC values for the glazing alone not "good enough". This is exactly what
> the reviewer is trying to get at.
>
> I'd hardly call NFRC certification rare. In the State of Washington NFRC
> certification has been required for all glazing assemblies for over 10
> years.
>
> How do you justify certifying that your projects have met the mandatory
> provisions of ASHRAE 90.1 without NFRC data?
>
> *Robby Oylear, LEED**®** AP BD+C*
>
> *Mechanical Project Engineer*
>
> *Energy Analyst*
>
> * *
>
> *D* 206-788-4571 | *C* 206-354-2721
>
> *www.rushingco.com* <http://www.rushingco.com/>
>
> On Fri, Jul 29, 2011 at 11:12 AM, Carol Gardner <cmg750 at gmail.com> wrote:
>
>>
>>
>> On Thu, Jul 28, 2011 at 5:40 AM, Omar Katanani <omar at ecoconsulting.net>wrote:
>>
>>> Dear all,
>>>
>>>
>>>
>>> Thank you for your responses.
>>>
>>>
>>>
>>> 1. Are the NFRC testing and the values in table A8.2 used for the
>>> Baseline, Proposed, or both scenarios?
>>>
>>> For the baseline windows, Appendix G gives the following instructions:
>> Fenestration
>> U-factors shall match the appropriate requirements in Tables 5.5-1 through
>> 5.5-8. Fenestration SHGC shall match the appropriate requirements in
>> Tables
>> 5.5-1 through 5.5-8.
>> They are silent about frames but I would use one, match the frame width of
>> your proposed window. Use an Aluminum frame with no thermal break.
>>
>>>
>>>
>>>
>>>
>>> 1. Let’s say I do not have NFRC test results and decide to use the
>>> values in table A8.2. For a clear double glazed and metal frame type, I get
>>> an assembly U-factor of 5.1. How can I input this into eQUEST? As far as I
>>> know, I can enter the glass properties and the frame properties. Do I have
>>> to play with the glass properties and check the LV-D report for the
>>> calculated Assembly u-value?
>>>
>>> A U of 5.1 does not make sense. Are you sure this isn't R?
>>
>>
>>>
>>>
>>> Similarly, for the baseline, Tables 5.5-1 to 5.5-8 of ASHRAE 90.1 provide
>>> the assembly u-values for vertical glazing. How can I enter these values
>>> into eQUEST?
>>>
>>>
>>>
>>> 1. I am attaching the specs of the proposed glazing. These numbers
>>> are for the glass only (note that the u-values reported are NFRC ones).
>>> Additionally, I know that the frame will be aluminium. Do I still need NFRC
>>> U-values for the whole assembly, or is the NFRC usually for the glass only?
>>> If yes, how can I calculate the whole assembly U-value (given that eQUEST
>>> doesn’t have the ability to calculate this)
>>>
>>>
>> For your proposed building I highly recommend you use LBNL's Window
>> program. In it you can select your window type, e.g. casement, picture,
>> etc,, select your glass from their glass library, which is huge and
>> definitely includes Solarban, and then model your frame using whatever
>> information the architect gives you related to thermal breaks and spacers.
>> After you run your window in the program you can select to save it to a DOE
>> 2 report which will automatically go into your DOE 2 Window folder. Then you
>> just have to select it from the pull down menu.
>>
>> Otherwise, input your glass values, as you are already, *and* input your
>> frame data, the same data you got from your architect, and model it that
>> way. When you look at your LV-D report you will likely see a variety of U
>> values. That's because they will vary based on window size.due to the frame
>> effect. You need to have a frame.
>>
>> As far as NFRC, your Solarban glass data is NFRC rated which should be
>> good enough, I think. It's rare in commercial buildings to have a rating for
>> the entire window.
>>
>> Carol
>>
>>>
>>>
>>>
>>>
>>> Thanks for clarifying this, as my project is outside the US and we are
>>> not too familiar with standards such as NFRC.
>>>
>>>
>>>
>>> Best regards,
>>>
>>> Omar
>>>
>>> ___________________________
>>>
>>> Omar Katanani
>>> Sustainable Design Engineer
>>>
>>> Email: omar at ecoconsulting.net
>>>
>>>
>>>
>>> EcoConsulting (Lebanon)
>>>
>>> Nahas Building, 4th floor
>>>
>>> 4 St-Maron Street / Georges Haddad Avenue
>>>
>>> Postal Code: 2028 5806 SAIFI
>>>
>>> Beirut, Lebanon
>>>
>>> Tel: +961 (0) 1 971 266
>>> Mobile: +961 (0) 3 045 045
>>>
>>>
>>>
>>> EcoConsulting (UK) Ltd
>>> 28 Marshalsea Road
>>> London, SE1 1HF
>>> Tel: +44 (0) 207 939 0989
>>> Fax: +44 (0) 207 939 0981
>>>
>>> Website: www.ecoconsulting.net
>>>
>>>
>>>
>>>
>>> ------------------------------
>>>
>>> *From:* Robby Oylear [mailto:robbyoylear at gmail.com]
>>> *Sent:* 28 July 2011 00:53
>>> *To:* Omar Katanani
>>> *Cc:* Brad Robinson; equest-users at lists.onebuilding.org
>>>
>>> *Subject:* Re: [Equest-users] URGENT: Window U-values: Total window
>>> assembly v/s Glass only
>>>
>>>
>>>
>>> Omar,
>>>
>>>
>>>
>>> To directly answer your question:
>>>
>>>
>>>
>>> "I’m assuming that, given that I entered the u-values for the glass
>>> only, and then I entered information about the frame, then I need not worry
>>> about any conversions in U-values, *since eQUEST has all the necessary
>>> information to calculate the equivalent u-value of the whole pane + frame
>>> assembly,*right?"
>>>
>>>
>>>
>>> No. Your method will result in an assembly U-value based on your input
>>> glass conductance and whatever default frame properties that the eQUEST
>>> wizard will use. I have never tried to let eQUEST determine an assembly
>>> value, as NFRC values are required for LEED and code compliance studies. I
>>> would not be surprised if the values eQUEST is calculating (shown in LV-D
>>> and LV-E reports like previously mentioned) are much different than what
>>> you'll actually see in the test results.
>>>
>>>
>>>
>>> Again, NFRC values are a LEED requirement, so unless you're just doing
>>> preliminary analysis for a client, you need to receive NFRC simulation
>>> reports or certified product directory numbers in accordance with NFRC 100.
>>>
>>>
>>>
>>> *Robby Oylear, LEED® AP BD+C*
>>>
>>> *Mechanical Project Engineer*
>>>
>>> *Energy Analyst*
>>>
>>> * *
>>>
>>> *D* 206-788-4571 | *C* 206-354-2721
>>>
>>> *www.rushingco.com* <http://www.rushingco.com/>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> On Wed, Jul 27, 2011 at 2:44 PM, <omar at ecoconsulting.net> wrote:
>>>
>>> Dear Robby,
>>>
>>> Yes, I am modeling for LEED purposes.
>>> I'll look into A8.2. But at least, is my method correct for the proposed
>>> scenario?
>>>
>>> Brad: I think you need to enter the center of glass u-value in the "Glass
>>> Type", and then enter the frame properties in the "Window" properties...
>>>
>>> Best,
>>> Omar
>>>
>>>
>>>
>>> Quoting Brad Robinson <brad.robinson at yahoo.com>:
>>>
>>>
>>>
>>> Is the u-value listed for a manufacturer and specific model on the NRCAN
>>> website centre of glass or overall assembly? Many windows are custom made
>>> to suit so I am unclear if each individual custom window would need to be
>>> tested.
>>>
>>>
>>>
>>> In eQuest, when entering the window, if the u-value represents the whole
>>> window, including frame, do you need to enter a frame width, conductance etc
>>> as well under the Window Frame section under Window Properties? Thanks.
>>>
>>>
>>> Brad Robinson
>>>
>>>
>>>
>>> ________________________________
>>> From: Robby Oylear <robbyoylear at gmail.com>
>>> To: Omar Katanani <omar at ecoconsulting.net>
>>> Cc: equest-users at lists.onebuilding.org
>>> Sent: Wednesday, July 27, 2011 12:32:08 PM
>>> Subject: Re: [Equest-users] URGENT: Window U-values: Total window
>>> assembly v/s Glass only
>>>
>>>
>>> Omar,
>>>
>>> The answer depends on the purpose of your study. If you're trying to get
>>> results for a client on the impact of the glazing on their energy
>>> performance, this may be adequate. Make sure you've entered in the framing
>>> information properly (metal vs. non-metal).
>>>
>>> I'd recommend opening up your simulation output results file (xxxx.SIM)
>>> and going to the either the last page of the LV-D report or sort through
>>> your LV-E report to see what value eQUEST has calculated. Compare these
>>> values to the ASHRAE Fundamentals results for overall assembly values
>>> including frame to see how close you've come. I would not blindly trust
>>> that eQUEST will give you an appropriate overall assembly value based on
>>> entering only the center of glass number.
>>>
>>> However, if this is for a LEED study, this is not adequate. This an
>>> excerpt from an e-mail I sent out recently regarding LEED and NFRC
>>> requirements.
>>>
>>> In order to meet LEED EAp2 Minimum Energy Performance, the project must
>>> comply with all mandatory provisions of ASHRAE 90.1-2007. Section 5.4.2
>>> Fenestration and Doors requires that fenestration performance be determined
>>> per section 5.8.2. Section 5.8.2.4 U-factor requires that the U-factor for
>>> the overall fenestration area (including framing) be determined in
>>> accordance with NFRC 100. If you do not have NFRC data available, values
>>> from section A8.2 are the only acceptable alternative.
>>>
>>> Robby Oylear, LEED®AP BD+C
>>> Mechanical Project Engineer
>>> Energy Analyst
>>>
>>>
>>> D206-788-4571 |C206-354-2721
>>>
>>>
>>> www.rushingco.com
>>>
>>>
>>>
>>>
>>>
>>> On Wed, Jul 27, 2011 at 8:14 AM, Omar Katanani <omar at ecoconsulting.net>
>>> wrote:
>>>
>>> Dear all,
>>>
>>>
>>> I have a small question regarding entering
>>>
>>> window properties to eQUEST:
>>>
>>>
>>> I have read a lot of emails in the forum
>>>
>>> discussing NFRC testing, LBNL Window 5 import, and other topics that I
>>> haven?t
>>> paid attention to before.
>>>
>>>
>>> The way I modelled my windows is the
>>>
>>> following:
>>>
>>>
>>> 1. I have manufacturer?s specifications listing the glass
>>> U-values, not the total assembly.
>>> 2. In the ?Glass Types? (eQUEST Detailed Mode), I created glass
>>> types, and entered the glass conductance, visible transmittance, SC, and
>>> emissivity from the manufacturer?s details I have.
>>> 3. When creating windows, I specify which glass type (from the
>>> ones I created in step 2), in addition to the frame width and conductance.
>>>
>>>
>>>
>>> I?m assuming that, given that I
>>>
>>> entered the u-values for the glass only, and then I entered information
>>> about
>>> the frame, then I need not worry about any conversions in U-values, since
>>> eQUEST has all the necessary information to calculate the equivalent
>>> u-value of
>>> the whole pane + frame assembly, right?
>>>
>>>
>>> I appreciate your feedback / comments
>>>
>>> today if possible, as this has become really urgent!
>>>
>>>
>>> Many thanks,
>>> Omar
>>> ___________________________
>>> Omar Katanani
>>> Sustainable Design Engineer
>>> Email: omar at ecoconsulting.net
>>>
>>> EcoConsulting (Lebanon)
>>>
>>> NahasBuilding, 4th floor
>>>
>>>
>>> 4 St-Maron Street/ Georges Haddad Avenue
>>> Postal Code: 2028 5806
>>>
>>> SAIFI
>>>
>>> Beirut, Lebanon
>>> Tel: +961 (0) 1 971 266 <%2B961%20%280%29%201%20971%20266>
>>> Mobile: +961 (0) 3 045 045
>>>
>>> EcoConsulting (UK) Ltd
>>> 28 Marshalsea Road
>>> London, SE1 1HF
>>> Tel: +44 (0) 207 939 0989
>>> Fax: +44 (0) 207 939 0981
>>> Website: www.ecoconsulting.net
>>>
>>>
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>>
>>> _______________________________________________
>>> Equest-users mailing list
>>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>>> To unsubscribe from this mailing list send a blank message to
>>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>>
>>>
>>
>>
>> --
>> Carol Gardner PE
>>
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110729/bce1a912/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110729/bce1a912/attachment-0002.jpeg>
More information about the Equest-users
mailing list