[Equest-users] Saving Schedules to Library
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Mon Jun 13 14:39:36 PDT 2011
Word!
On Mon, Jun 13, 2011 at 2:11 PM, Nick Caton <ncaton at smithboucher.com> wrote:
> To Pasha’s concerns – I am personally very comfortable with the import
> function placing things in the appropriate locations, but that is based
> solely on my own personal investigation and tinkering with the program when
> I first explored the possiblities. I’ve yet to come across any issues, but
> until you do feel comfortable, you can always import to a copy of your
> actual project to verify the result before proceeding. Constructions end up
> listed with existing constructions, annual/week/day schedules end up with
> their counterparts, and so forth as far as I’ve been able to tell.
>
>
>
> Order of systems where OA-FROM-SYSTEM is in play is an independent and
> isolated quirk of the eQuest/DOE2 that you may have to deal with even if you
> don’t use importing, and neither is it terribly difficult to resolve once
> it’s brought to your attention (likely on trying to simulate). I guess I’m
> just saying that this particular issue isn’t a reason to avoid importing
> where it can save time…
>
>
>
> That said, while I have imported portions of airside/waterside systems into
> new projects for modification/use, I have *always* built DOAS systems “from
> scratch” on a project-by-project basis, when I am modeling them distinct
> from the systems served. Importing an independent DOAS and its components
> would be a tricky endeavor, to be sure... I will likely consider importing
> DOAS setups more viable and time-efficient if/when an independent DOAS
> system type defined in future versions of eQuest/DOE2.
>
>
>
> To Richard – creating an .inp snippet of simpler items like a schedules or
> constructions becomes time-efficient the very first time you import into
> another project, I promise ;)! Once you have a smallish library of
> re-useable constructions/schedules, you will be able to transform multiple
> 5-to-30 minute exercises into a matter of a few clicks.
>
>
>
> To be clear, that’s no reason to go cataloguing a library of everything you
> “might” use in the future (that would quickly become time-inefficient), but
> building your library from past projects as the need arises is probably the
> balanced approach. For example… “Ah, I wish I had a schedule to describe
> this photocell/timer-controlled exterior lighting… Wait! I did that legwork
> for an earlier model! *open/copy/paste/save/import* Life is good!” If
> your memory isn’t razor sharp, the other “ideal” time to catalogue .inp
> snippets would be at the conclusion of a project, while the model is fresh
> in your mind, to identify what items required research/legwork you’d like to
> avoid in the future.
>
>
>
> Generally – any development of DOE2/eQuest is welcome in my eyes, great or
> small, and . I trust where both “difficult” and “simple” developments are
> on the table, the priorities of addressing fundamental limitations against
> user interface improvements will be weighed appropriately against the
> resources that become available. I’m just counting myself lucky to be
> modeling in an era that doesn’t require punch cards and ticker tape =)!
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER
>
>
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* Pasha Korber-Gonzalez [mailto:pasha.pkconsulting at gmail.com]
> *Sent:* Monday, June 13, 2011 1:32 PM
> *To:* Richard Auffermann
> *Cc:* Nick Caton; Paul Riemer; equest-users at lists.onebuilding.org
>
> *Subject:* Re: [Equest-users] Saving Schedules to Library
>
>
>
> If I had to bet on the developers including that function soon, I would say
> you'd be luckier to bet that your grandkids will see that feature...here's
> why:
>
>
>
> The great developers of eQuest are by foundation HVAC designers---they are
> not software developers or programmers by trade or even family tree. ;)
>
>
>
> Therefore this is how it goes for most simulators who are using eQuest
> today. If I had the chance to talk to Jeff & Steve and guys I would be
> more inclined to ask them to quickly develop a way that VRV systems and DOAS
> systems can be easily modeled in DOE-2.2/eQuest, RATHER than ask them to
> spend thier valuable development time creating a library function in eQuest.
>
>
>
> If you had your 'druthers' which would you choose?
>
>
>
> That's also why some of the other basic functions in eQuest, (i.e. it looks
> like a spreadsheet, but doesn't act like one...) are not further developed
> or available either. There is more than enough work to be done to just get
> the guts of DOE-2.2 working to support the industry for what it needs,
> rather that improve upon the administrative tools in eQuest itself.
>
>
>
> It's a funny situation, but remember that this whole building simulation
> things is literally a new frontier that we are all discovering an we are
> still only in it's infancy.
>
>
>
> Pasha :)
>
> On Mon, Jun 13, 2011 at 12:25 PM, Richard Auffermann <
> rauffermann at dagherengineering.com> wrote:
>
> Thanks Everyone,
>
>
>
> I just spent some time generating a few schedules and testing things out,
> this could really cut down time once everything is set up. While this has
> impressive capabilities like bring in an entire second building, it is
> overly complicated for doing the simple things, like importing a schedule or
> construction that you will use for every model.
>
>
>
> I just find it weird and a bit of a tease to have the ‘Save to Library’
> option present but not actually usable, are they ever going to include that
> functionality?
>
>
>
> Richard Auffermann
>
> Design Engineer
>
> DAGHER ENGINEERING, PLLC
>
> 29 Broadway, New York, NY 10006
>
> T. 212.480.2591 x122
>
> F. 212.480.2654
>
> rauffermann at dagherengineering.com
>
> www.dagherengineering.com
>
>
>
> Save Trees, Consider the Environment. Please print only when necessary.
>
>
>
> This email and any attachments may contain confidential or proprietary
> information and use or distribution is strictly prohibited. If you are not
> the intended recipient, please notify us and delete. Dagher Engineering,
> PLLC has no responsibility for errors or discrepancies that may occur in the
> electronic transmission of data.
>
>
>
>
>
> *From:* Nick Caton [mailto:ncaton at smithboucher.com]
> *Sent:* Monday, June 13, 2011 1:25 PM
> *To:* Paul Riemer; Pasha Korber-Gonzalez; Richard Auffermann
>
>
> *Cc:* equest-users at lists.onebuilding.org
>
> *Subject:* RE: [Equest-users] Saving Schedules to Library
>
>
>
> The import function really is the cat’s meow ;). It’s a great timesaver,
> even if you do need to break out your text editor (once only!).
>
>
>
> See attached thread from a while ago where I walk everyone through the
> process, and touch on the possibilities.
>
>
>
> Starting a personal collection of .inp snippets (schedules, equipment,
> constructions, and so on) is a major mile marker on the path to becoming a
> great eQuest modeler – welcome to the club =).
>
>
>
> ~Nick
>
> [image: cid:489575314 at 22072009-0ABB]
>
> * *
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
>
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Paul Riemer
> *Sent:* Monday, June 13, 2011 12:07 PM
> *To:* 'Pasha Korber-Gonzalez'; Richard Auffermann
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Saving Schedules to Library
>
>
>
> Collectively, we have previously suggested to create snippet text.inp files
> and then use the Import command rather than copy paste within a text editor.
> So you might have a library of inp files for things like constructions,
> schedules, hourly reports, and utility rates (but you can reference saved
> ones within the wizard too). Of course some things are order dependent like
> your OA source system being ahead of your destination system so if you want
> a DOAS snippet, you may need to manually place that within in the project
> .inp file.
>
>
>
> If you like having an inp snippet library then you might also try carrying
> the parametric run description (prd) file from project to project.
>
>
>
> *Paul Riemer, PE, LEED AP*
>
> *DUNHAM*
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Pasha
> Korber-Gonzalez
> *Sent:* Monday, June 13, 2011 11:36 AM
> *To:* Richard Auffermann
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Saving Schedules to Library
>
>
>
> At this point in time....Yes, that is the best that we can do as far as I
> know. I had a client once who told me they were using, or pulling in thier
> own company's "library" data info, but I don't know if this was in the
> formal sense of using the Libraries in eQuest or if they created a seprate
> file that could be read by thier eQuest files to pull in the equipment info
> they wanted.
>
>
>
> The only way I know of and use right now is the copy paste method in the
> input file....
>
>
>
> Pasha
>
> On Mon, Jun 13, 2011 at 9:44 AM, Richard Auffermann <
> rauffermann at dagherengineering.com> wrote:
>
> I am generating schedules for my model and was hoping to save them so I do
> not have to recreate them all the time. There is an option to “Save to
> Library” but it is greyed out and cannot be selected. I looked in the
> archive and the only emails on this topic say that you can only save the
> text from the input file and copy this into new models. Is this the best we
> can do?
>
>
>
> Richard Auffermann
>
> Design Engineer
>
> DAGHER ENGINEERING, PLLC
>
> 29 Broadway, New York, NY 10006
>
> T. 212.480.2591 x122
>
> F. 212.480.2654
>
> rauffermann at dagherengineering.com
>
> www.dagherengineering.com
>
>
>
> Save Trees, Consider the Environment. Please print only when necessary.
>
>
>
> This email and any attachments may contain confidential or proprietary
> information and use or distribution is strictly prohibited. If you are not
> the intended recipient, please notify us and delete. Dagher Engineering,
> PLLC has no responsibility for errors or discrepancies that may occur in the
> electronic transmission of data.
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110613/84bf5bd4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110613/84bf5bd4/attachment-0002.jpeg>
More information about the Equest-users
mailing list