[Equest-users] IPLV Curve Fit
Robby Oylear
robbyoylear at gmail.com
Wed Jun 15 14:35:51 PDT 2011
Hi Nick,
In my experience the EIRFLPR curve is not looking for a normalized
efficiency. If you look at the default chiller curves you'll notice that
the EIRFPLR correction factor actually decreases as you approach zero
part-load. This would not make sense if it was an EIR correction factor, as
the efficiency of the chiller actually increases as part-load decreases (at
least with a variable speed chiller).
The chiller EIRFPLR curve is actually looking for a ratio of current kW
power draw divided by kW power draw at full-load.
The thread from when I was struggling through this for the first time myself
is located here:
http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/2008-February/006827.html
<http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/2008-February/006827.html>Not
all that useful as I believe someone assisted me through the process
off-list, but the conclusion remains the same.
-Robby
On Wed, Jun 15, 2011 at 1:55 PM, Nick Caton <ncaton at smithboucher.com> wrote:
> Hi Lyle,
>
>
>
> I think you need to review a little further before proceeding. Read
> through the attached discussion from the bottom up. This discussion
> diverges a bit (as performance curve topics usually do) but I think you’re a
> bit ahead of the curve so to speak (har har!) in recognizing what the IPLV
> numbers really mean. Plugging in your IPLV values as coefficients for a
> cubic equation (where f(x) = Ax^3+Bx^2+Cx+D) is pretty much wildly different
> from the correct course of action, but you’re definitely in the ballpark’s
> parking lot ;).
>
>
>
> Ultimately, you (and others – listen up!) will probably have the best shot
> of getting it right on the first go if you visualize what you’re doing in
> excel. That’s what worked for me when I was climbing this mountain:
>
>
>
> · Assemble your part load percentages and corresponding EER’s in
> excel
>
> · Stop and review what the curve in eQuest is looking up, and from
> what variable(s). You can glean this from the title of the default curve
> used… In this case, you want eQuest to determine EIR each hour as a
> function of Part load (EIRfPLR).
>
> · Knowing that, convert convert your EER values to to EIR
>
> · Now, normalize each EIR value to the ARI value*. If the EER at
> ARI is 9, and your 50% part load EER is 6, then the normalized vaule is 6/9
> = 0.67. This normalized number is actually a multiplier of sorts that
> eQuest will apply against your specified ARI efficiency in the chiller input
> window. If none of this is making sense, go back further and review my
> “recommended reading” list in a thread called “Chiller curves, oh boy!” from
> sometime last year in the archives.
>
> · Using excel, plot these normalized efficiencies (y-axis) against
> the part load ratios (x-axis) with a scatter chart.
>
> · Right click and add a curve-fit to the series. In the dialog,
> try making it third order (quadratic) and see if you get a good fit. Check
> the option to display the curve equation.
>
> · Voila, there are your four coefficients (A,B,C,D – see eQuest’s
> curve inputs to be sure you know which is which in the quadratic format) for
> eQuest! You’ve also developed a visual check to ensure the numbers make
> sense.
>
>
>
> *Important: You MUST work from ARI-condition data points, and normalize to
> the ARI condition, and specify your chiller’s capacity/efficiency at ARI
> conditions, if you are trying to only make PLR curves without doing a full
> set of custom curves. The reasons why are complex, and I’ve already nearly
> written a book on the matter in the archives if you’re itching to know why
> ^_^. If you want to specify your chiller around design conditions, then
> it’s all or nothing (library curves) with regard to custom curve creation!
>
>
>
> A general statement/consolation to everyone: We all have to crawl before we
> can run! Make no mistake, coming to a true fundamental understanding of
> custom curves in eQuest/DOE2, to the point you can manipulate and even
> create them on your own, is no small feat. They should give out medals!
> The best way to develop this skill set is to accept you will probably screw
> it up a few times to start, look hard at your results, and read up on the
> literature/advice that’s out there in order to learn what it is that you
> personally don’t know. Once you come around to understanding what you do
> know, and more importantly what you know that you don’t know… (Donald
> Rumsfeld would make a good energy modeler, lol<http://en.wikiquote.org/wiki/Donald_Rumsfeld>),
> it’s all downhill from there, and you can begin to ask the right questions
> of yourself and others to bridge your personal gaps. Making mistakes is
> commendable, provided you resolve to learn from them!
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER
>
>
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com* *
>
>
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER
>
>
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Robby Oylear
> *Sent:* Wednesday, June 15, 2011 2:43 PM
> *To:* Lyle Keck
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] IPLV Curve Fit
>
>
>
> Lyle,
>
>
>
> The short answer is no. IPLV cannot be used to create performance curves
> in eQUEST.
>
>
>
> Part-load curves are a strange animal in eQUEST. You'll need cooperation
> from the chiller manufacturer to get the correct data. You need to have
> enough data to describe the way energy varies as a function of part-load,
> chilled water supply temp, and outside air temperature. Take a look at the
> attached spreadsheet which can be used to create curves in eQUEST. The data
> in yellow should be entered by the manufacturer or manufacturer's rep. The
> data in red should be entered into eQUEST.
>
>
>
> If you look into the formulas, you'll note that EIR-FPLR is actually not an
> EIR factor, it is based on the power draw of the equipment at part-load
> compared to at full-load. This throws a lot of people off as it is not
> described that way in the help documentation.
>
>
>
> The interesting question that arises when working with custom part-load
> curves is how accurate does the eQUEST default performance curve model the
> required IPLV for the baseline per ASHRAE 90.1? In my experience the
> default curve is approximately 10% worse than the IPLV requirement.
>
>
>
> Hope this helps,
>
>
>
> Robby Oylear, LEED AP BD+C
>
> Mechanical Project Engineer
>
> Energy Analyst
>
> Rushing
>
>
>
> On Wed, Jun 15, 2011 at 10:59 AM, Lyle Keck <lkeck at aeieng.com> wrote:
>
> All,
>
> I am trying to create a part load curve for an air-cooled screw chiller. I
> have the EER & COP data for 100%, 75%, 50%, and 25% loading.
>
>
>
> I have read through the various posts in the archives and I am still unsure
> if I should input this data as ‘raw data’ or ‘coefficients’
>
>
>
> From previous posts:
>
>
>
> IPLV (or NPLV) = 0.01A+0.42B+0.45C+0.12D
>
> Where:
>
> A = COP or EER @ 100% Load
>
> B = COP or EER @ 75% Load
>
> C = COP or EER @ 50% Load
>
> D = COP or EER @ 25% Load
>
>
>
> It is my understanding that EIR-PLR curves give the EIR as a function of
> part load ratio.
>
>
>
> SO, if I create a ‘cubic’ curve with input type ‘curve coefficients’, and
> input a=(1/COP-100%), b=(1/COP-75%), c=(1/COP-50%), and d=(1/COP-25%) and
> specify this curve as the EIR - f(part load ratio) curve, would that be
> accurate?
>
>
>
> Additionally, this chiller has a condenser water temp of 95 degF and design
> conditions that differ from AHRI conditions (design EWT=58 degF and LWT=44
> degF)
>
> Do these values have direct correlation to the curve creation ? Or can the
> condenser and CHW temp simply be defined in the ‘basic specifications’ tab
> for the chiller, and the EWT defined via the CHW loop deltaT?
>
>
>
> I know this topic has been widely discussed, but I am still uneasy about
> the actual inputs for the creation of the part load performance curve.
>
>
>
> Any input, or reference to a previous post would be appreciated.
>
>
>
> Thanks in advance,
>
>
>
> *Lyle Keck** *
> SustainablE Systems Analyst
>
>
>
> *AEI* | AFFILIATED ENGINEERS, INC.
> Westlake Center Office Tower, 1601 Fifth Avenue, Suite 1400 | Seattle, WA
> 98101
>
> P: 206.256.0800 | F: 206.256.0423
> lkeck at aeieng.com | *www.aeieng.com*
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> ---------- Forwarded message ----------
> From: "Paul Diglio" <paul.diglio at sbcglobal.net>
> To: "Nick Caton" <ncaton at smithboucher.com>, <
> equest-users at lists.onebuilding.org>
> Date: Sat, 26 Feb 2011 07:15:46 -0500
> Subject: Re: [Equest-users] using IPLV in eQuest
> Nick:
>
> I agree with your analysis. A curve built using different kW/Ton for the
> four different load ratios that are used in the IPLV calculation would be
> sufficient.
>
> I would just be careful when creating a curve that uses different condenser
> water supply temperatures. It is more of a design issue. There has to be a
> reason why the condenser water temperature varies. It will effect the lift
> and kW/Ton. For example, current chillers will tolerate a much lower
> condenser water temperature. Does this mean that it is more efficient to
> provide the lower condenser water temperature? Not necessarily, since
> energy will be wasted running the cooling tower fans to achieve the lower
> temperature and energy will be wasted for the hot-gas bypass to bring the
> condenser pressure up.
>
> In my experience, the lower condenser water temperature is most often an
> issue on chiller start-up in cold weather. Some chillers will surge until
> the chiller warms the condenser water loop. Surging sounds like someone
> with advanced COPD breathing.
>
> So, if Rohini's chillers are supplied with a nearly constant condenser
> water temperature, the EIR f(PLR&Lift) would not be critical.
>
> Please see attached modeling data from Trane for a CVHE 450 ton chiller.
> All the data to build the various curves is shown. Note the difference in
> condenser bundle pressure drop for standard flow v. minimum flow. Much
> energy can be saved with a variable condenser water pumping strategy.
>
> This data was used to calculate the loss of chiller efficiency due to
> reduced condenser water flow. In this particular project, I had three
> existing chillers. Total savings realized by the variable condenser water
> scenario was 250,000 kWh/Year. The reduced chiller efficiency consumed
> 50,000 kWk per year so the net energy savings was 200,000 kWh/Year. Notice
> that the condenser water temperature varies in the data. That was based on
> the maximum heat rejection of the towers during the cooling season with a
> minimum of 65 degrees condenser water supply temperature. If I assumed a
> constant 78 degrees condenser water supply temperature the kW/Ton values
> would be much different.
>
> It takes a little time to find the right person to provide this chiller
> data, but it is well worth it.
>
> Paul
>
>
> ------------------------------
> *From:* Nick Caton <ncaton at smithboucher.com>
> *To:* Paul Diglio <paul.diglio at sbcglobal.net>;
> equest-users at lists.onebuilding.org
> *Sent:* Fri, February 25, 2011 4:38:43 PM
> *Subject:* RE: [Equest-users] using IPLV in eQuest
>
> Thanks very much for the informed response, Paul!
>
>
>
> With all respect, I want to be sure I’m picking up the right lessons here
> =):
>
>
>
> Accepting the arbitrary nature of IPLV ratings, what I’ve proposed for
> Rohini’s case is to define a curve that will utilize his model’s unique
> annual part-load profile (tossing IPLV’s weightings out the window), and
> would isolate the effects of PLR to make his equipment comparison.
>
>
>
> Am I correctly understanding that any comparative analysis that isolates
> only the effects of part-load in comparing two chillers is pretty much
> pointless?
>
>
>
> I am not trying to make a case that lift, variable flows, and their effects
> on capacity and efficiency are not important (and I have also experienced
> responses all over the map from different manufacturers). I agree that at
> least considering all of these in many cases is necessary when one wants to
> model accurate behavior, particularly from a commissioning/servicing
> context. With all other things being equal, I’m however proposing these
> factors shouldn’t be critical if the specific goal is to determine *whether
> chiller A or chiller B fits a model’s part load profile better*.
>
>
>
> So to clarify and make our bridges meet: Is it critical that Rohini
> creates an EIR-fPLR&dT curve for his analysis (between two screw chillers
> with everything else presumed identical), or is it fair to say this may be
> overkill considering what he’s trying to achieve?
>
>
>
> I for one will continue the good fight to obtain more solid input data for
> my curves, sometimes I have to settle for “the best I can get” with the
> people I’m supposed to be talking to, but your experiences are further
> motivation to try to find the right people =)!
>
>
>
> Thanks again,
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* Paul Diglio [mailto:paul.diglio at sbcglobal.net]
> *Sent:* Friday, February 25, 2011 2:58 PM
> *To:* Nick Caton; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] using IPLV in eQuest
>
>
>
> Nick:
>
> I come from a mechanical contracting and service background. Condenser
> water temperature is a hotly debated item. Some manufacturers define a very
> narrow range of acceptable condenser water temperature and others define a
> very narrow range of the temperature difference between entering and leaving
> condenser water temperature.
>
> During one investment-grade audit I performed recently, Trane told me that
> the condenser water dt can be no *less* than 5 degrees for maximum
> efficiency on the 650 ton CVHE chillers I was working with. The water
> temperature could be anywhere to 50-80 degrees. This machine had hot-gas
> bypass to keep the head pressure up.
>
> Other chillers that I have overhauled require a very narrow band of
> condenser water temperature, such as 75-78 degrees supply temperature. So
> modeling a wide condenser water range does not make much sense to me since
> it is not a real world application. The chillers I have worked on either
> have a tower bypass loop or a hot gas bypass to keep the condensing pressure
> up where it belongs. Energy is wasted when too cold a condenser water
> temperature is specified.
>
> Other manufacturers say the colder the better.
>
> Specifying variable primary chilled water flow and variable condenser water
> flow has a large impact on chiller efficiency. I ask the manufacturers to
> provide me the kW/Ton for minimum flow, standard flow and maximum flow for
> the evaporator and condenser bundles. A chiller that has an kW/Ton of .56
> at AHRI conditions can often have a 1.3 kW/Ton at minimum condenser flow (3
> gpm/ton) at 30% load.
>
> The IPLV is really a useless rating for a real world application since it
> assumes a certain percentage load a certain percentage of the time. It all
> depends on the design of the system and the load profile. It is a good
> rating to compare various chillers if they conform to the load profile. I
> see more chillers that run in the 40-60% range 90% of the time than I see
> chillers that match the IPLV conditions.
>
> During my investment-grade reviews with our local utility, the lift of the
> chiller is always an important consideration.
>
> There was an e-mail for someone, I believe York, that offered to model any
> manufacturers chiller on this forum a few months ago. I have had good luck
> getting the rep to provide the information that I requested as long as I
> find the right person.
>
> Paul
>
>
> ------------------------------
>
> *From:* Nick Caton <ncaton at smithboucher.com>
> *To:* Paul Diglio <paul.diglio at sbcglobal.net>;
> equest-users at lists.onebuilding.org
> *Sent:* Fri, February 25, 2011 2:50:44 PM
> *Subject:* RE: [Equest-users] using IPLV in eQuest
>
> Paul, I may not have been crystal-clear, but if someone is merely making a
> comparative analysis between two screw chillers, aren’t the relative effects
> of varying lift between the two chillers negligible? My general
> understanding is that lift is a more critical variable when comparing VSD
> centrifugal chillers… This is why I suggested a simpler EIR-fPLR curve
> would be sufficient in lieu of an EIR-fPLR&dT – I was trying to simplify
> Rohini’s comparative analysis.
>
>
>
> I’d agree that an EIR-fPLR&dT curve would be more precise and more
> appropriate if the goal is to better match the chiller behavior (and
> creating custom CAP-FT and EIR-FT would be even better), but I was thinking
> this would require an unnecessary amount of extra work for Rohini’s
> comparative purpose.
>
>
>
> My “suggested information to request” below for constructing EIR-fPLR&dT
> curves is based on my past experience with limitations of my local manf.
> rep’s software – they need to set certain items constant to get the numbers
> to crunch… Have you had luck collecting PLR runs where the evaporator
> and/or condenser temp was allowed to float? I’ve picked up through the
> lists that a better way to skin the cat may be to approach the chiller
> controls reps where they may exist, as they may have more flexible software…
>
>
>
> I throw this disclaimer out sometimes: I certainly haven’t been doing this
> for decades! If I’m misunderstanding something, I very much welcome
> corrections ;).
>
>
>
> Thanks,
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]
>
> * *
>
> *NICK CATON, E.I.T.*
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* Paul Diglio [mailto:paul.diglio at sbcglobal.net]
> *Sent:* Friday, February 25, 2011 12:44 PM
> *To:* Nick Caton; James Waechter; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] using IPLV in eQuest
>
>
>
> Actually what everyone is calling dt is more accurately referred to as
> lift. It is the difference between the saturated evaporating temperature
> and the saturated condensing temperature, which is different than the
> condenser water temperature and the evaporator water temperature.
>
> A more accurate curve can be built if you have the chiller manufacturer
> model both these variables for you, rather than leaving the evaporator water
> temperature constant and just varying the condenser water temperature. Any
> change in the evaporator pressure will effect the condensing pressure and
> any change in the condensing pressure will effect the evaporator pressure.
>
> Paul
> ------------------------------
>
> *From:* Nick Caton <ncaton at smithboucher.com>
> *To:* James Waechter <jamesw at McKinstry.com>;
> equest-users at lists.onebuilding.org
> *Sent:* Fri, February 25, 2011 1:21:42 PM
> *Subject:* Re: [Equest-users] using IPLV in eQuest
>
> James et al,
>
>
>
> Rohini will need to create performance curves to make this particular
> comparison. Otherwise using the default curves will result in identical
> part load performances.
>
>
>
> The following is excerpted from the following (short) recommended reading
> concerning what IPLV means:
> http://ashrae-cfl.org/2010/03/understanding-iplvnplv/
>
> IPLV (or NPLV) = 0.01A+0.42B+0.45C+0.12D
>
> Where:
>
> A = COP or EER @ 100% Load
>
> B = COP or EER @ 75% Load
>
> C = COP or EER @ 50% Load
>
> D = COP or EER @ 25% Load
>
> John is saying knowing only the IPLV and the 100% load condition efficiency
> (variable ‘A,’ above) is not enough information to extrapolate the IPLV
> curves to compare the two chillers.
>
>
>
> For the exercise of comparing the two non-centrifugal chillers of the same
> technology/type, I would just focus on making a custom EIR-FPLR (not
> EIR-fPLR&dT) for each chiller, and use the library CAP-FT AND EIR-FT curves.
> My understanding is the effects of temperature on capacity and EIR outside
> of centrifugal VSD chillers is negligible. NOTE: Whenever using any of the
> default library chiller performance curves, that means you MUST normalize to
> and specify the chiller at ARI conditions – those curves aren’t normalized
> to anything else.
>
>
>
> So! If you can find the IPLV A, B, C and D values for both chillers’
> curves, you could come up with your EIR-FPLR curve coefficients (*curve
> type = quadratic or cubic*) using a curve-fit in excel… or alternatively
> make eQuest figure the coefficients by entering those points as raw data.
>
>
>
> You may more easily just make your own curves, following John’s advice and
> getting part load unloading curves (100%, 90%, 80%... etc) held at a
> constant chilled & condenser temperature to match the ARI* conditions (85CWT
> if this is water cooled) at which you’re specifying the chiller
> capacity/EIR. Again, you could either go into excel, normalize the data
> (review DOE2 help entry for EIR-FPLR), make a scatter chart, and get the
> coefficients using a curve fit… or enter the data as raw points into eQuest
> and the coefficients will be figured by eQuest… whatever makes more sense to
> you.
>
>
>
> For others and personal future reference…. If you are looking to make an *
> EIR-fPLR&dT* curve (for centrifugal chillers or otherwise): Ask your rep
> instead for multiple (minimum 3) part load unloading runs, holding the
> delivered chilled water temp constant, and vary the condenser water
> temperature incrementally for each run (i.e. 85, 75, 65). Choose a range of
> CWT’s that cover the anticipated range to be encountered in the actual
> design. This will get you enough data to have the minimum 3 delta-T’s
> represented in your part load data points to build this curve correctly.
> You’ll be using eQuest “raw-data” entry method to make it generate the
> coefficients.
>
>
>
> ~Nick
>
>
>
> * Rather than ARI conditions (85F CWT), you could be normalizing to Design
> condition EIR/CAP, provided you’re making a full set of custom curves in the
> same fashion.
>
>
>
> [image: cid:489575314 at 22072009-0ABB]
>
> * *
>
> *NICK CATON, E.I.T.*
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *James Waechter
> *Sent:* Friday, February 25, 2011 10:55 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] using IPLV in eQuest
>
>
>
> John,
>
>
>
> If the only parameter Rohini enters into the program is the full-load EIR –
> which he said is the same for both chillers – how will eQuest know to bend
> the curves differently for the two chiller options. It is my understanding
> that program would use the same chiller efficiency curves for both machines
> even though their IPLVs are different.
>
>
>
> In order to overcome this issue, are you saying Rohini should get chiller
> performance data from each of the manufacturers and enter his own custom
> curves? I recall there was a discussion on that topic a few months back.
>
>
>
> Regards,
>
> James Waechter Jr., P.E., CEM, LEED A.P.
> Energy Engineer – Rocky Mountain Region
> p 303 215 4062 | m 727 686 3248
>
> *McKinstry*
> Consulting | Construction | Energy | Facility Services
>
> www.mckinstry.com
>
>
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *John Aulbach
> *Sent:* Friday, February 25, 2011 9:41 AM
> *To:* R B; eQUEST Users List
> *Subject:* Re: [Equest-users] using IPLV in eQuest
>
>
>
> Rohini:
>
>
>
> Won't happen. IPLV is a number which has one equation and 4 unknowns.
> Actually, three unknowns as you know the 100% point. You need a
> manufacturer's curve run at 85F constant condenser water temperature. Let
> eQuest do the curve bending after that. ARI curve won't work right.
>
>
>
>
>
> John R. Aulbach, PE, CEM
>
> Senior Energy Engineer
> ------------------------------
>
> *Partner** **Energy*
>
> 1990 E. Grand Avenue, El Segundo, CA 90245
> W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
>
> www.ptrenergy.com | jaulbach at ptrenergy.com
>
>
> ------------------------------
>
> *From:* R B <slv3sat at gmail.com>
> *To:* eQUEST Users List <equest-users at lists.onebuilding.org>
> *Sent:* Fri, February 25, 2011 7:25:18 AM
> *Subject:* [Equest-users] using IPLV in eQuest
>
> Hi All,
>
> I would like to compare two screw chillers with same full load kW/ton and
> different IPLV kW/ton. I am using the full load number for the EIR. Where
> can the IPLV number be used? Is there some way to scale the performance
> curves to reflect different IPLV's?
>
> -Rohini
>
>
>
>
> This email is the property of McKinstry or one of its affiliates and may
> contain confidential and/or privileged information. If you are not the
> intended recipient or have received this e-mail in error please notify the
> sender immediately and delete this e-mail. Any unauthorized copying,
> disclosure or distribution of the material in this e-mail is strictly
> forbidden.
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110615/19724dce/attachment-0002.htm>
More information about the Equest-users
mailing list