[Equest-users] Problem with changing HVAC system in Detailed DataMode
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Jun 23 09:56:33 PDT 2011
Morteza,
Make sure to delete the HW loop, boiler(s) and pump(s) if you are not
assigning any systems/coils/loads to the loop, or you will get an error.
It helps to delete the child components first (boiler pump, then boiler)
before you delete the loop.
Regards,
Bill
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Morteza
Kasmai
Sent: Thursday, June 23, 2011 12:23 PM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] Problem with changing HVAC system in Detailed
DataMode
Hello all,
I am following the Equest-users Digests for a while and learn allot.
Thanks to every one of you for all your helpful comments and guides.
Now I am working on the energy model of an existing warehouse to be
renovated as an office building. For baseline model, there are five
packaged rooftop VAV systems with Hot-water fossil fuel boiler (System 5
per ASHRAE 90.1). However, for the Design case five rooftop systems with
fossil fuel furnace has been defined.
I am in Detailed Date Edit and when I change the system heat sources
from Hot Water Loop to Furnace, I get an error (Terminated Due to
Errors). Actually, if I leave just one system heat source as HWL it
would be OK and I don't face any errors, but when all heat sources have
been changed to furnace and there is no Hot water Loop assigned to any
system, there will errors.
Please find the attached pd2 and inp files of the project.
Your comments would be greatly appreciated.
Morteza
Morteza Kasmaei
Architect, LEED(r) AP BD+C
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110623/d1b932c8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110623/d1b932c8/attachment-0002.jpeg>
More information about the Equest-users
mailing list