[Equest-users] Furnace AFUE, Et, HIR and furnace fuel auxiliary
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Jun 23 11:02:09 PDT 2011
Carol,
I'll defer to Bruce's expertise on furnaces. Between his comments below,
and the note in 90.1, Table 6.8.1E that I quoted below (in my second
question), it would appear that we should use 0 as the default eQUEST
value for Furnace Fuel Auxiliary. You can still enter a non-zero value
if modeling an old furnace, using your pilot light calculator to show
savings as an ECM. Now Google "energy use of air conditioner crankcase
heater" and help me figure out the eQUEST default for CRANKCASE-HEAT. ;)
Bill
From: Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Thursday, June 23, 2011 1:43 PM
To: Bishop, Bill
Cc: Bruce Easterbrook; eQUEST Users List
Subject: Re: [Equest-users] Furnace AFUE, Et, HIR and furnace fuel
auxiliary
Hi Bill,
I agree with your conclusions but got curious about boilers and pilot
lights and their usage. I have to admit to being fairly ignorant when it
comes to gas using equipment. So I did what I usually do and Googled
energy use of a pilot light and came across this nice little website:
http://energyexperts.org/EnergySolutionsDatabase/ResourceDetail.aspx?id=
4407
that had a link to a nice little calculator that can be used to
calculate pilot light energy use:
http://www.wisconsinpublicservice.com/home/gas_calculator.aspx
When you are in the calculator there is "more info" next to the furnace
line and it includes the following information "natural gas furnaces and
boilers have been required to have pilotless ignitions since 1980". That
would mean that the eQUEST default should be modified to be 0, right?
Carol
On Wed, Jun 22, 2011 at 6:43 AM, Bishop, Bill <
wbishop at pathfinder-ea.com> wrote:
Thanks Bruce.
I appreciate your insight on the reasonable range of furnace
efficiencies. I was more concerned with how to model the baseline per
minimum ASHRAE efficiencies. Using my question numbering, I'm going with
these answers:
1.) Warm Air Furnace
2.) No pilot light
3.) HIR=1.25
Bill
From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
Sent: Tuesday, June 21, 2011 8:57 PM
To: Bishop, Bill
Cc: eQUEST Users List
Subject: Re: [Equest-users] Furnace AFUE, Et, HIR and furnace fuel
auxiliary
Hi Bill,
I don't have a project to pull up to get to these inputs. I believe I
normally enter the AFUE, and 78% is an medium oil number and a low gas
number. Typically most gas units on the market will give you a 92% AFUE
for a condensing unit and a few are running in the 94% range. Oil you
can get into the 84% range. Don't do condensing oil, no one is using
the correct steel in the heat exchangers and they rot out after a few
years. No units run with a pilot light anymore and you can see why, it
is all spark ignition. I normally use a warm air furnace on a PSZ. Use
78% for oil and 92% for gas, no pilot light for either. You can adjust
everything later on the heating/unitary power tab. Grain of salt, I
don't do LEED work, just 90.1. For the project I have open I have a HIR
of 1.08 and 0 auxiliary, gas. So I probably input 92% AFUE in the
wizard, no pilot light.
Bruce Easterbrook P.Eng.
Abode Engineering
On 21/06/2011 10:12 AM, Bishop, Bill wrote:
When selecting "furnace" for the heat source, eQUEST adds 800 Btu/h for
furnace fuel auxiliary (pilot light) as default. The default 800 Btu/h
adds 12% to my baseline heating energy, so it is not trivial.
ASHRAE Standard 90.1, Table 6.8.1E lists minimum furnace efficiency
requirements.
What should I enter for Furnace HIR and Furnace Fuel Auxiliary for
Baseline System 3 (PSZ-AC) and the new 90.1-2010 Baseline System 9
(Heating & Ventilation; Warm-air furnace, gas-fired)?
First, which equipment type applies? Table 6.8.1E has three gas-fired
equipment types - Warm Air Furnace, Warm Air Duct Furnace, and Warm Air
Unit Heaters. I think both Systems 3 and 9 would be Warm Air Furnace,
since packaged (System 3) and ventilation (System 9) systems would seem
to preclude duct furnaces and unit heaters.
Second, does the note, "Units must also include an interrupted or
intermittent ignition device (IID)" mean that no pilot light should be
modeled? This note to Table 6.8.1E does not apply to Warm Air Furnaces
<225,000 Btu/h in 90.1-2004 or 90.1-2007, but applies to all Warm Air
Furnaces in 90.1-2010. This is a LEED 2.2 project but the building is
currently under construction.
Third, Warm Air Furnace minimum efficiency is 78% AFUE or 80% Et .
Should I use HIR=1.282 (78%) or HIR=1.25?
Thanks for your thoughts,
Bill
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110623/4f3a6e5d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20862 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110623/4f3a6e5d/attachment-0002.jpeg>
More information about the Equest-users
mailing list