[Equest-users] Sizing Ratio
Nick Caton
ncaton at smithboucher.com
Tue Jun 28 06:57:30 PDT 2011
If the 17 floors have a collective design cooling load of 100 tons, then
you'll end up with a system capacity of 1,700 tons by doing that to the
sizing ratio... I don't think that's your intent!
If you wish for your heating/cooling capacities to be auto-sized with
some "fluff" to account for extreme heating/cooling conditions and
internal loads that your TMY-based model might not reflect, then by all
means give your auto-sized capacities a sizing factor higher than 1.
If the modeled loads are 1/17 of what they should be in the end, I think
you would need to address the loads directly before trying to adjust the
system.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of DongEun
Kim
Sent: Tuesday, June 28, 2011 12:09 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Sizing Ratio
Hi all,
Can anyone help me with this two question?
As I model a high-rise building using"Floor Muliplier", I have a floor
(middle) which actually represent the load for 17 floors.
Now I want to link this floor(s) to a certain HVAC system.
Can I simply put "17" in System Sizing > Sizing Ratio ?
Thank you in advance !
~DE
Kim, DongEun(DE) | Research Engineer, LEED AP
Annex R&D Institute, HIMEC(Hanil Mech. & Elec. Consultants)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/db1778e4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/db1778e4/attachment-0002.jpeg>
More information about the Equest-users
mailing list