Javed,
The guideline was created to create the chiller plant defined by ASHRAE
90.1 Appendix G which is used for LEED modeling and accepted by USGBC.
This information is located in Appendix G Section G3.1.3.7 through
G3.1.3.10, which if you don't have a copy of Appendix G, it is a
must-have. It basically states for plants greater than 300 tons, you
will have variable speed pumps on the secondary loop instead of the
pumps riding the pump curve. You will also have 2 chillers for plants
>300 tons. This is all stated in the Appendix G document. Hope this
helps!
Thanks,
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239
MatthewRLarson at Eaton.com
www.eaton.com/energysolutions
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of javed
iqbal
Sent: Monday, June 27, 2011 10:37 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chiller Baseline Methodology
Hi All,
I have found this guideline for Baseline Chiller Plant
Modeling for capacity <300 TR. I just wanted to know is it acceptable by
USGBC? What will be the methodology for Plant >300 TR?
Please find the parent link for this attachment.
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010
-November/006884.html
Thanks
--
Javed Iqbal, LEED AP, CEA
Project Manager
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/f5dcb0ab/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/f5dcb0ab/attachment-0002.jpeg>
More information about the Equest-users
mailing list