As Nick previously mentioned, you may need to use different areas for
different aspects of the project (lighting, PV, energy, ventilation, etc.)
For the energy modeling portion, you should probably talk to your project
design engineer as the building construction you describe is a bit unusual.

 

Going back to the fundamental heat flow equations that simulations use, the
heat flow calculation is based on some area  and includes outside and inside
air films, wall assembly construction, material properties, heat transfer
path, etc.  For your specific building, the thermal properties of the wall
material may not offset the additional wall areas due to the thickness of
the wall.  In a normal size building, the wall area of the corners is
usually small in comparison to the total wall area so the corner details
become negligible.  Since you've said the building area changes by 4% when
you include the wall thickness, you are correct to raise the question.  I
think the question needs to go back to the design engineer who is familiar
with your specific building construction.

 

In a very simple example, when specifying insulation for piping, it is
actually possible to increase the heat-loss by adding too much insulation
because of the increase in surface area relative to the insulation
thickness.  I know your building is not a pipe (and probably not round) but
this simple example just goes to show how important it is to understand the
limitations of the equations being used and not assume that what is
negligible for 8-12" thick wall construction, is also negligible for 24"
thick wall construction.

 

Regards,

 

Michael Hardy, PE, F.NSPE 
Sr. Mechanical Engineer
Black Oak Engineering, Inc.
Cell 503.314.5244 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Praveen
Jain
Sent: Tuesday, March 01, 2011 4:44 AM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] External wall area for simulation

 

Thanks Nick for good explanation.

Actually in my project we are using almost 2ft wide external walls to get
the effect of thermal mass. if I consider external wall area in eQUEST model
my area deviation is almost 4% and mismatch in conditioned area is more than
this. So project energy consumption would be more and also not able to match
TR for the project.
Actually we are also planning to go for 2.5% renewable energy credit, if I
consider external wall than PV cost would be more.

Can I exclude external wall area for eQUEST modeling ?

--
With Thanks and Regards
Praveen 

On Mon, Feb 28, 2011 at 10:02 PM, Nick Caton <ncaton at smithboucher.com>
wrote:

Hi Praveen,

 

I've copied below a discussion from some time back outlining my general
practice for "where to draw the line" when it comes to envelope/wall
boundaries.  This may be generally useful and seems to answer at least part
of your inquiry.

 

When I'm doing electrical and/or HVAC design alongside the model, my area
takeoffs for each inevitably will match up, because I hate doing the same
work twice.  

 

I use the outermost surfaces when defining my building footprint and
midpoints for all internal partitions for all calcs.  Space-by-space LPD
calcs in a strict reading do not require the space areas to be measured to
the outermost surface of an exterior wall (they do say to use the midpoint
of interior partitions, as of 90.1-2007).  I'd feel comfortable saying the
extra square-footage "handicap" I'm imposing on myself as a lighting
designer is an insignificant fraction in 99.9% of cases when determining
baseline LPD.   

 

Inevitably, areas summed for all spaces in a building between architects,
HVAC, and lighting designers will not match - that's a fact of life and in
my book that's okay, so long as nobody is way off.  Model reviewers will
inevitably/reliably gripe when the numbers don't match exactly, and it's
usually  an easy thing to either fix or explain after the fact.  If you to
try to make everyone use the same numbers from the DD/CD design phases,
you've chosen a losing battle.  For my part in the role of the project's
energy modeler, I'm satisfied to allow my fellow designers do their own
calcs, and just ensure nobody is way off along the way. quibbles over small
differences in the final tallies, if they come up, are easy to reconcile.

 

~Nick

 

Error! Filename not specified.

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

 <http://www.smithboucher.com> www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Praveen
Jain
Sent: Monday, February 28, 2011 3:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] External wall area for simulation

 

Dear All

 

While modeling in eQUEST should we include external wall area or not?

While creating single line diagram I exclude external wall and draw sld on
inner of external wall to match conditioned area.

But for lighting power density calculation ASHRAE 90.1 user manual suggest
to including external wall area. 

We are getting mismatch in area calculation for all HVAC, Lighting and
Architectural design sides.

 

Can anyone suggest what correct way of modeling in eQUEST ?

-- 
With Thanks and Regards,
Praveen K. Jain
Roorkee

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Wednesday, August 04, 2010 1:20 PM
To: John Aulbach; Nijenmanting, F.C.; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] area of (internal) partitions

 

Filique,

 

This sounds a lot like a question I brought up when I was getting started
with eQuest and energy modeling in general:  What is "standard practice"
regarding where the inter-zonal and footprint boundaries are defined,
relative to actual wall thicknesses?  The quick answer is that there aren't
any hard/fast answers to this.  It was a good discussion and is probably
archived in [bldg-sim] if anyone cares to dig around.

 

In short:  

1.       eQuest areas correspond to the polygons used to define the floor
areas/building footprint.  These polygons are defined by the shapes defined
or traced from a CAD file in the wizards.  I'm pretty sure (someone correct
me if I'm wrong) the floor area taken up by internal partitions (which have
thickness) on the floor slab is NOT subtracted from the total area, so if
you double the thickness of your internal partitions you will not see a
change reflected in space areas.  This is normally not a big deal in the
context of thermal modeled behavior, but if you have many unusually thick
partitions (1ft or more deep), you might want to either account for them by
modeling them as unconditioned zones between spaces.  

2.       Regarding "best practice," here's a set of general guidelines that
would apply to various loads & modeling software packages (beyond eQuest),
prioritizing the interest of modeling with thermal accuracy:

a.       Define interior partitions using the midpoint between the two
surfaces.  This is generally not terribly critical - I will take small
liberties on this to reduce the number of vertices and simply actual
internal zones.

b.      Define the building footprint areas using the outermost surface.
This is more important as you want to accurately model the actual amount of
surface area subject to exterior loads.

c.       Define top of each zone (in the z-axis) using the top surface
elevation the respective floor or roof construction.

3.       On a related note, this ties into the general advice to not use
energy modeling programs with the intent to create perfect 3D
representations of your buildings.  If you need a pretty picture, they make
3D modeling software for that purpose.  When it comes to building
geometries, simplicity is a virtue, and ASHRAE will even back you up on that
one (re: 90.1 User's Manual).  Avoiding overly-accurate building geometries
lets you spend more time modeling the more critical building elements of a
building's energy behavior (loads/systems/schedules/etc).

 

Best wishes,

 

~Nick

 

Error! Filename not specified.

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @  <http://www.smithboucher.com>
www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Wednesday, August 04, 2010 12:15 PM
To: Nijenmanting, F.C.; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] area of (internal) partitions

 

Filique:

 

Can you rephrase your question, please?  I don't understand how doubling the
size of your internal partitions decreases your floor area. The eQuest floor
areas are (to my undestandinding), from the outside of outside walls to the
"outside" of any internal partitions IN THE SPACE THAT PARTITION RESIDES.
You can have only one internal wall separating two adjacent spaces.

 

Others may comment.

 

John R. Aulbach, PE, CEM

Senior Energy Engineer

  _____  

Partner Energy

1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745

www.ptrenergy.com <http://www.ptrenergy.com/>  | jaulbach at ptrenergy.com
<mailto:%7C%20jaulbach at ptrenergy.com> 

 

 

  _____  

From: "Nijenmanting, F.C." <F.C.Nijenmanting at student.tue.nl>
To: "equest-users at lists.onebuilding.org"
<equest-users at lists.onebuilding.org>
Sent: Wed, August 4, 2010 12:15:19 AM
Subject: [Equest-users] area of (internal) partitions

Hello all,

I have a question about the area which is calculated by equest.
Does it take into account the width of internal partitions?
In reality, if I would double the size of my internal walls, my actual floor
area decreases.
But I could not find differences in the floor area calculated by Equest if I
change the thickness of my walls.

A similar question accounts for the external partitions. For drawing the
ground plan, should I therefore take the internal boundary, external
boundary or middle line?

Kind regards,
Filique
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

 




-- 
with regards,
Praveen K. Jain